Esteemed wrenches, We're working often in the Bahamas and now that net metering is approved there, the inspectors are far behind in their comprehension. That said, we are currently required to combine the utility with the PV in a main load center before going to the generator transfer switch. I have a 400 amp rated load center with a 200 amp, 120/208 main breaker on it, as well as four 60 a, 3 pole breakers that will be fed from four 10 kw inverters. My question is, will it be necessary to use wire rated at 400 amps or can I use wire rated for the main breaker? Thank you for your input. It might be a stupid question, but I am stymied here....it might just be the Lyme, not sure.....oh, and it's CEC 2015 down there, but I suspect it will align with NEC 2014.
Thanks again, Daryl DeJoy NABCEP Certified PV Penobscot Solar Design _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org