Hi All, Is anyone out there familiar with PV Powered inverters? If so, is it possible to adjust the voltage setpoints? The installation manual I downloaded off their website says it is adjustable, but tech support claims that it is something that they intended to do and never got around to. I cannot tell if that is true, or if they just don't want to let a random installer not familiar with their product make adjustments.
The issue here is that we have installed an add on PV system. They already have high grid voltage, and the old inverter is on a pole mount ~250' from the meter. With both systems in place the voltage frequently gets too high. I've already opened the voltage window on the new SMA inverter and I would like to do the same for the customer on the old PVP-4800 inverter rather than telling them that we'll need to re-pull much larger wires or move the inverter closer to the meter. Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org