Hello Wrenches,

I'm picking this thread back up now that more
information has become available.

What I learned from talking with an AEP engineer
is that the issues with the delta configuration
on local AEP systems is that the transformers are
wye-delta. The AEP system is wye on the utility
side and delta on the load side. Originally it
appeared that the issue was that the customer had
requested 120/240 V loads, so they center tapped
one phase of the 240 V delta 3 phase and grounded
it to create a neutral. Apparently, if they
ground the delta, they won't ground the wye.

According to the engineer I spoke with, the wye
windings, with no ground reference, could be kept
energized indefinitely from inverter backfeed
into the delta side in the event that the utility
lost one phase. I would think the voltage would
go high on the open line and any connected
inverters would shut down from high voltage. This
may not be quick enough to meet UL 1741 requirements.

He said that "all sorts of weird problems" can
occur if both sets of windings are grounded. He
didn't go in to what the problems would be.Does anyone know?

AEP also said that having an ungrounded delta
system, and creating 120 V power through a
transformer would not be acceptable. At that
point, I was told that the utility will not
supply an ungrounded delta system. Problems I can
see with an ungrounded delta include the issue
that a ground fault on one leg would not activate
overcurrent protection. (Maybe they could have a
ground fault alarm system). Another problem is
that a neutral could not be run to the service,
as required by the NEC, since there would be no neutral.

Has anyone backfed a wye-delta transformer? Does
any utility supply an ungrounded delta? What are
the problems with grounding the center point of
the wye and grounding the delta?

Thanks,

Drake

At 11:50 AM 6/5/2017, you wrote:
We have done many high-leg delta installations
with both single phase and three phase inverters here in the Bay Area.
Â
Besides the normal stinger-leg type issues of
trying to install a single phase 120 volt load
across the high leg, I’m not aware of any
particular problems. Certainly we see many
existing old services where the high leg spots
are left blank and only two of the three phases
are used for branch circuits. It seems like
perhaps this would cause load balancing type
issue with the utility. I’m by no means
familiar with the ins and outs of what causes transformer problems, however.
Â
August
Luminalt
Â
From: RE-wrenches
[mailto:[email protected]] On Behalf Of Jeff Clearwater
Sent: Monday, June 05, 2017 8:19 AM
To: RE-wrenches
<<mailto:[email protected]>[email protected]>
Subject: Re: [RE-wrenches] 4 Wire Delta
Â
Hi Drake,

Souther Cal Edison allowed us to do a High-Leg
Delta - sharing this in the chance like William
that at least you can say others have - can't imagine what their issue is.

Best,

Jeff

Drake wrote:

Hello Wrenches,

I've recently learned that AEP, our utility
company, believes it is unsafe to backfeed a 4
wire delta transformer. Does anyone know what the issues are?

Thanks,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
Â
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
Image removed by sender.

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>www.avast.com


_______________________________________________
List sponsored by Redwood Alliance
Â
List Address:
<mailto:[email protected]>[email protected]
Â
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
Â
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
Â
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Â
Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org
Â
Â
--
Jeff Clearwater
Village Power Design
Renewable Energy Design & Installation
Ecovillage Design Consultant

Former NABCEP Certified - 2003-2012
Licensed Solar Contractor in CA - C-46
<http://www.villagepower.com>www.villagepowerdesign.com
413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Content-Type: image/jpeg; name="image001.jpg"
Content-Disposition: inline; filename="image001.jpg"
Content-ID: <[email protected]>
X-Attachment-Id: 82cef4cbd5ee3dac_0.1


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to