Most generators with  microprocessor controller have a steady & unavoidable 
phantom load these days.

 

----------------------------------------------------------------------------

Dana Orzel                       Great Solar Works, Inc. 

208.721.7003                       [email protected]

Idaho Contractor - # 028765          Idaho PV # 028374

NABCEP # 051112-136                       www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Drake
Sent: Tuesday, July 11, 2017 6:11 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Generator choice for Sunny Island

 

What is the standby current draw on this unit. In the past, that has been an 
issue with Kohler. 

At 06:01 PM 7/10/2017, you wrote:



All - update for those of you interested, we are starting the portal 
installation tomorrow (with a Sunny Island for better or worse) and ended up 
going with a Kohler 14RESA propane generator. This should be 2-wire start, ok 
at 100% duty cycle 120 v, and CARB compliant. If all goes as planned we'll be 
up and running next week and I'll keep you posted.

http://www.kohlergenerators.com/home-generators/products/14RESA

-August

August Goers

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525

www.luminalt.com <http://www.luminalt.com> 

 

On Fri, Jun 23, 2017 at 3:46 PM, Dave Angelini Offgrid Solar 
<[email protected] <mailto:[email protected]> > wrote:

I did a few projects for Yosemite. Then I used the EU6500i which is now

the EU7000i. Never had anyone ask. and that you will find is the issue. In

my county of Mariposa they will issue a certificate of occupancy on a

house running a generator for final approval. Pretty lax about it all. If

I go across the county line into Tuolumne everything is hard to do. Geeze

an offgrid generator...Use Honda or design so that you don't need one :)

Dave Angelini / Offgrid Solar



> Hi Gary and All â€â€œ

> 

> 

> 

> We looked into the EcoGen unit, but the 6kW is discontinued and the 15kW

> EcoGen is not rated to be sold in California. Bummer.

> 

> 

> 

> Speaking of California, do any of you know about the CARB compliance

> issues

> on selecting a generator for an offgrid renewable project? We had one

> generator rep tell us that only a Tier 4F CARB generators are legal for

> use

> with offgrid in California, but I can’t ¢t find anything online to clarify.

> Since this project is in the National Parks, we need to make sure we

> don̢۪t

> > have any compliance issues. If anyone knows anything about what kind of

> CARB compliance is or isn̢۪t required, I, I̢۪d love to hear about it.

> >

> 

> 

> Cheers!

> 

> 

> 

> August

> 

> 

> 

> *From:* RE-wrenches [ mailto:[email protected] 
> <mailto:[email protected]> ] *On

> Behalf Of *Gary Willett

> *Sent:* Friday, June 16, 2017 7:58 AM

> *To:* [email protected] 
> <mailto:[email protected]> 

> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island

> 

> 

> 

> AUGUST:

> 

> The Generac EcoGen is dual-fuel capable (NG or LP), comes in 6kW and 15kW

> versions, is 2-wire start, can be field-configured for either 120V or

> 240V.

> It's not "portable" as it does not have wheels. It's transportable though

> based on its footprint and weight. Also, it was specifically designed and

> warranteed  for off-grid applications.

> 

> Regards,

> 

> Gary Willett PE

> Icarus Engineering LLC

> 

> On 6/16/17 9:36 AM, Kevin Pegg wrote:

> 

> You could use a 2 -> 3 wire converter such as the Atkinson GSCM module

> that

> will take the 2 wire output from the SI and convert to 3-wire to control a

> gasoline generator such as the Honda EU7000 series, or Cummins/Onan makes

> a

> good line of gasoline generators. It may be very hard to find a gas

> generator that has 2 wire native remote start. That is more common with

> larger propane or diesel generators.

> 

> 

> 

> Kevin

> 

> 

> 

> *From:* RE-wrenches [mailto: [email protected] 
> <mailto:[email protected]> 

> < [email protected] 
> <mailto:[email protected]> >] *On Behalf Of *August 
> Goers

> *Sent:* June-16-17 7:22 AM

> *To:* RE-wrenches < [email protected] 
> <mailto:[email protected]> >

> < [email protected] 
> <mailto:[email protected]> >

> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island

> 

> 

> 

> Thanks for the good feedback folks!

> 

> 

> 

> We are using a Sunny Island setup because we had access to a free Sunny

> Island and Sunny Boy being scrapped from another site. Otherwise I was

> definitely planning on going with a Outback DC coupled system.

> 

> 

> 

> I think the trick here is trying to find a portable generator that has a

> two-wire start option. I̢۪m looking throurough the usual genny suppliers and

> nothing has presented itself so far. Anyway, I’™ll keep looking and will

> check out Chris̢۪ suggestion on the nexus controtroller and Generac propane

> unit as well.

> 

> 

> 

> FYI, here is a link to what the portal is like. Itâ€ââ„¢s going in National

> Park

> land by the Golden Gate Bridge so I hope we can pull it together!

> http://www.sharedstudios.com/ 

> 

> 

> 

> August

> 

> Luminalt

> 

> 

> 

> 

> 

> *From:* RE-wrenches [ mailto:[email protected] 
> <mailto:[email protected]> ] *On

> Behalf Of *Chris Mason

> *Sent:* Friday, June 16, 2017 4:56 AM

> *To:* RE-wrenches < [email protected] 
> <mailto:[email protected]> >

> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island

> 

> 

> 

> To my limited mind, the whole 120V sunny island setup is a disaster. Why

> not install a DC coupled 8KW Outback Radian and solve all your problems.

> USe any 240V generator, although finding a 2 wire start gasoline unit may

> be hard. I would use a Nexus controller generac propane generator with

> propane tank, all mounted on the container. I would never design anything

> to use gasoline, it's too dangerous.

> 

> 

> 

> On Fri, Jun 16, 2017 at 7:19 AM, Matthew Sirum <[email protected] 
> <mailto:[email protected]>  >

> wrote:

> 

> Greetings August,

> 

> Great thoughts and comments from Brian!  I would also suggest speaking

> with the generator manufacturers' tech/engineering folks regarding the

> 120VAC configuration and to confirm 2-wire start set up once you have

> a brand and model or two in mind.  Generator parts and service

> availability in the region of the project may also drive brand

> selection.  If you need to maximize the inverter's battery charging

> capabilities (depending on battery system charging requirements) you

> may end up needing to look at generators in the 7.5 kW to 8.0 kW

> capacity range to allow for headroom in generator output loading.

> 

> Also; I am curious how you arrived at an AC coupled design for this

> project.  I do not know any of the details or specific projects goals

> you are working with, but I would potentially consider a DC coupled

> system design...  DC/DC charge controller(s) would keep the battery

> system charged (and any DC loads operable) even if the Sunny Island

> and/or Sunny Boy(s) have a failure or is taken offline.  If most of

> the AC loads are 120VAC I would consider keeping the inverter AC

> output circuit 120VAC and install a dedicated transformer solely for

> the 240VAC load....  Or perhaps consider a 120/240VAC inverter model.

> Depending on the overall situation a DC coupled system could be more

> resilient.  The dedicated transformer for the 240VAC load could also

> potentially help make the system more robust.  Also; I have spoken

> with a number of folks who have told me they wish the Sunny Island had

> more/better features for generator integration.  I'd like to hear more

> from those who have plenty of experience designing and installing

> systems with Sunny Islands and generators to learn what the current

> thoughts and issues are.

> 

> I hope some of these thoughts may be helpful.

> 

> Best regards,

> 

> ----MATT

> 

> Matthew Sirum

> P.O. Box 1227

> Greenfield, MA 01302-1227Â  USA

> phone: +1.413.773.0611

> email: [email protected] <mailto:[email protected]> 

> 

> 

> --------Â  Original Message Below --------

> 

> [RE-wrenches] Generator choice for Sunny Island

> August Goers august at luminalt.com <http://luminalt.com> 

> Thu Jun 15 09:02:41 PDT 2017

> 

> Hi Wrenches, especially those of you who work on off-grid projects,

> 

> We have an upcoming off-grid project where we will be powering a storage

> container with electronics in it. The loads are mostly 120 volt but there

> is a 240 volt heat pump that might occasionally run. We̢۪re AC coupling

> > the

> Sunny Island with a Sunny Boy PV inverter. So, weâ€â„„¢ll be installing a

> Outback PSX-240 autoformer to bump the Sunny Islandâ€ââ„¢s output from 120 to

> 240 volt.

> 

> We need to select a generator for backup. We need a two-wire electric

> start

> (in order to be controlled by the Sunny Island) and preferably a generator

> that is okay just running 120 volt loads since the Sunny Islands input is

> only 120 volt. Something in the 3 kVA -7 kVA range should be fine.

> 

> Does anyone have experience or ideas about what kind of two-wire start

> generator we might select?

> 

> Thanks,

> 

> August

> 

> Luminalt

> _______________________________________________

> List sponsored by Redwood Alliance

> 

> List Address: [email protected] 
> <mailto:[email protected]> 

> 

> Change listserver email address & settings:

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

> 

> List-Archive:

> http://www.mail-archive.com/[email protected]/maillist.html 

> 

> List rules & etiquette:

> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

> 

> Check out or update participant bios:

> www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

> 

> 

> 

> 

> 

> --

> 

> Chris Mason

> 

> NABCEP Certified Solar PV Installerâ„¢

> 

> Solar Design Engineer

> 

> Generac Generators Industrial technician

> 

> 

> 

> www.cometsolar.com <http://www.cometsolar.com>  < 
> http://www.cometenergysystems.com <http://www.cometenergysystems.com/> >

> 

> 264.235.5670 <tel:264.235.5670> 

> 

> 869.662.5670 <tel:869.662.5670> 

> 

> Skype: netconcepts

> 

> 

> 

> 

> _______________________________________________

> 

> List sponsored by Redwood Alliance

> 

> 

> 

> List Address: [email protected] 
> <mailto:[email protected]> 

> 

> 

> 

> Change listserver email address & settings:

> 

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

> 

> 

> 

> List-Archive:

> http://www.mail-archive.com/[email protected]/maillist.html 

> 

> 

> 

> List rules & etiquette:

> 

> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

> 

> 

> 

> Check out or update participant bios:

> 

> www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

> _______________________________________________

> List sponsored by Redwood Alliance

> 

> List Address: [email protected] 
> <mailto:[email protected]> 

> 

> Change listserver email address & settings:

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

> 

> List-Archive:

> http://www.mail-archive.com/[email protected]/maillist.html 

> 

> List rules & etiquette:

> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

> 

> Check out or update participant bios:

> www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

> 

>



Dave Angelini Offgrid Solar

"we go where powerlines don't"

http://members.sti.net/offgridsolar/

e-mail  [email protected] <mailto:[email protected]> 

text 209 813 0060 <tel:209%20813%200060> 

_______________________________________________

List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:

www.members.re-wrenches.org <http://www.members.re-wrenches.org> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html 

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings: