Hello boB and Steve,

I haven't been able to make it to the site yet, but so far, no more reports of spikes. I plan to try boB's suggestion of shutting off the grid input while it is selling, to see what happens.

The spike did only last one second, so I don't think it is a chemical whip effect. If the spike only lasted a fraction of a second, wouldn't the Mate 3 still show the event lasting a second, since that is its lowest level of granularity?

The array size is 2240 W and the Concorde battery bank is 305 AH at 48 V for a C/6.5 charge rate. The battery bank should have been fully charged. If the grid went down and the Radian quit selling during a heavy selling period, could that not cause a 1 second voltage spike, or should the Classic catch it instantaneously?

Thanks,

Drake

At 11:49 PM 7/18/2017, [email protected] wrote:


The Classic can overshoot but not very much, normally.

I would try this...

Sell to grid while watching the battery voltage and then turn the inverter breaker off

and see what the battery voltage does. If the battery voltage rises to the mid 60V range

from a low sell voltage of around 52 or 53V, then something is really amiss.

If the system has been in service for some time, you might also check the capacity of

the batteries. They should not easily allow 65-ish volts. I don't think that the

FM's communication can respond  to keep spikes from happening any better

than it could without communications.  Data packets just don't come all that

often.

boB

On 7/18/2017 5:25 PM, Jerry Shafer wrote:
Wrenches
The Outback system with grid connection would be programmed for grid connection all the way from the inverter to the Outback FM CC, using a midnite CC this option may not be possible resulting to a CC push if the grid disconnects resulting in a spike. the disconnect might be from settings to tight or as it was said utility spikes. You might thing that the battery bank should take it up but internal resistance in the battery or to it may prevent it. The other thing I would look at is connections, if there is any resistance in a connection this could happen.

On Mon, Jul 17, 2017 at 2:36 AM, Drake <<mailto:[email protected]>[email protected]> wrote:
Hello Wrenches,

My client reported seeing an overvoltage error message on her Mate 3 on a Radian system. The Radian is selling to the grid and is being fed by a Midnite Classic 200. It has shown two spikes so far, the last one going to 67 volts and lasting 1 second. The batteries are Concorde AGM, 305 AH.

Does this momentary spike seem like a problem or a warning of problems to come?

Thanks,

Drake

_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org





_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to