I think the factors you have to consider include:
- the number of conductors in the trench,
-are they in a jacketed cable,
-are they separate conductors,
-are they considered "closely bundled",
-what is the distance of the conductor system once it exits the ground
before entering a conditioned space, and will it be in conduit.
Chris
On 8/5/2017 5:36 PM, Corey Shalanski wrote:
How should we treat direct burial wires in a trench for ampacity
derating purposes?
- Should they be considered "in a raceway or cable"? [NEC 310.15(B)(3)(a)]
- If it is determined that "spacing" must be maintained, what minimum
spacing is acceptable/permissible?
I would be interested to hear what means and methods others have used
to deal with this issue.
--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org