Hi Wrenches - We have an ~3 year old grid tied battery backup system with a SMA Sunny Island 4548 and Power-One (now ABB) PVI-5000 inverter. There is also an Outback PSX-240 to boost the Sunny Island voltage to 240 volts.
We recently returned to the site for an annual service call and tested the system by simulating a power outage. The Sunny Island kicked in just fine and provided stable voltage for the backup loads. However, the ABB tries to connect and immediately we see that voltage and frequency of the Sunny Island grid start to rapidly fluctuate. I have a feeling that my Fluke meter is not capturing the fluctuations properly, but I was seeing voltage fluctuate in the 238 to 242 volt range and frequency rapidly fluctuate between 59 and 61 Hz. The ABB connects for a minute or two and then gives us a grid out of range error. This occurs when we have lots of irradiance and also under relatively low light conditions. I've already been on the phone with SMA tech support several times and verified that all the Sunny Island settings are good. Has anyone else seen this type of instability issue and did you find a fix? We might need to install a Sunny Boy. Thanks, August *August Goers* Luminalt
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org