Thanks everyone for the comments.
I knew that PG&E no longer requires a visible blade lockable disconnect on all 
residential installations.  I did not know that they still require them for 
supply side taps until I started filling out the application for step 2 of the 
NEM process.  It sounds like no one has gotten a variance on this requirement, 
so I probably won't try to.
All the best,Jerry Caldwell
 

    On Wednesday, October 4, 2017 6:33 AM, August Goers <[email protected]> 
wrote:
 

 Hi Jerry -

This chart from PG&E may be helpful:

https://www.pge.com/includes/docs/pdfs/b2b/interconnections/AC-Disconnect.pdf

For all supply side connections, PG&E requires a fusible visible blade
lockable disconnect.

https://www.pge.com/includes/docs/pdfs/shared/customerservice/nonpgeutility/electrictransmission/handbook/060559.pdf

-August


*August Goers*

On Tue, Oct 3, 2017 at 7:25 PM, Jerry Shafer <[email protected]>
wrote:

> Jerry
> Historically the utilities require a bladed disco, we had one on a military
> base which required a breaker by the base  but we also were required to
> install a visible fused disco no breaker because is approved by that
> utility. Seeing is Believing when it comes to discos.
> Jerry
>
> On Tue, Oct 3, 2017 at 3:16 PM, Gary Willett <[email protected]
> >
> wrote:
>
> > Jerry:
> >
> > I don't know about PG&E, but here in Texas, a VLLD (Visible Lockable
> > Labeled AC Disconnect) is required for the PV system AC disconnect. They
> > want to see a switch on which it can be seen that it is off with the
> > dead-front cover closed, and that can be locked-out using their lock in
> the
> > off position. These requirements usually are fulfilled with a knife
> switch
> > type disconnect.
> >
> > The PV system AC disconnecting means has to have an SCCR (short circuit
> > current rating, in kA) that will handle the same available short circuit
> > current as the main service disconnecting means. Usually, that's readily
> > achievable with fuses.
> >
> > It may be possible to mount a service entrance rated circuit breaker in a
> > dedicated enclosure (visible/lockable) if PG&E says OK. But then you may
> > run into NEC 110.10 listing issues unless the enclosure's SCCR is based
> on
> > assembly testing by a NRTL to UL 508A.
> >
> >
> > Regards,
> >
> > Gary Willett
> > Icarus Engineering / Solar Services LLC
> >
> >
> > On 10/3/17 12:21 PM, Jerry Caldwell wrote:
> >
> >> Dear Wrenches with experience in PG&E territory:
> >> I'm installing a system with a line side tap.  Can I use a small
> subpanel
> >> with room for only one circuit breaker instead of a fused disconnect?
> The
> >> NEM application, step 2 requires you to select a fused disconnect from
> >> their list of approved devices.  Does anyone have experience with PG&E
> >> granting a variance on this requirement?
> >>
> >> Thanks in advance.  Any help is appreciated.
> >> Jerry Caldwell510.205.2798
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> List Address: [email protected]
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: http://www.mail-archive.com/re
> >> [email protected]/maillist.html
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> >>
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: [email protected]
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: http://www.mail-archive.com/[email protected].
> or
> > g/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/[email protected].
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



   
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to