There may be two tests here.
1)I think you can use 705.12(D)(2)(3)(c)
The sum of the ampere ratings of all overcurrent devices on panelboards,
both load and supply devices, excluding
the rating of the overcurrent device protecting the busbar, shall not
exceed the ampacity of the busbar. The rating of the
overcurrent device protecting the busbar shall not exceed the rating of
the busbar. Permanent warning labels shall be applied
to distribution equipment that displays the following or equivalent wording:
WARNING:
THIS EQUIPMENT FED BY MULTIPLE SOURCES.
TOTAL RATING OF ALL OVERCURRENT DEVICES,
EXCLUDING MAIN SUPPLY OVERCURRENT DEVICE,
SHALL NOT EXCEED AMPACITY OF BUSBAR.
The warning sign(s) or label (s) shall comply with 110.21(B).
2) I think though, that you also need to check the busbar rating of
panel that is supplying power to this inverter combiner panel so that
125% of the inverters' output from the combiner panel plus the main
breaker on the supplying panelĀ does not exceed the busbar rating of the
supplying panel.
Chris
On 10/17/2017 5:36 PM, Corey Shalanski wrote:
*Scenario*
- 600A *dedicated PV* subpanel w/ (6) 100A circuit breakers, each
feeding a 60kW inverter (72.2A rated output)
- Subpanel is fused at 600A and connects to a larger main
distribution/combiner panel along with other similarly configured subpanels
*Question*
- Must the main panelboard be sized based on the combined total of OCPDs
protecting the subpanels, e.g. 600A + 600A + 600A + 600A = 2400A main panel
rating?
- Or can the main panelboard be sized based on the combined total of
inverter output ratings feeding the panel, e.g. 433.2A + 433.2A + 433.2A +
433.2A = 1732.8A main panel rating?
--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org