There may be two tests here.

1)I think you can use 705.12(D)(2)(3)(c)

The sum of the ampere ratings of all overcurrent devices on panelboards, both load and supply devices, excluding the rating of the overcurrent device protecting the busbar, shall not exceed the ampacity of the busbar. The rating of the overcurrent device protecting the busbar shall not exceed the rating of the busbar. Permanent warning labels shall be applied
to distribution equipment that displays the following or equivalent wording:
WARNING:
THIS EQUIPMENT FED BY MULTIPLE SOURCES.
TOTAL RATING OF ALL OVERCURRENT DEVICES,
EXCLUDING MAIN SUPPLY OVERCURRENT DEVICE,
SHALL NOT EXCEED AMPACITY OF BUSBAR.

The warning sign(s) or label (s) shall comply with 110.21(B).


2) I think though, that you also need to check the busbar rating of panel that is supplying power to this inverter combiner panel so that 125% of the inverters' output from the combiner panel plus the main breaker on the supplying panelĀ  does not exceed the busbar rating of the supplying panel.

Chris


On 10/17/2017 5:36 PM, Corey Shalanski wrote:
*Scenario*

    - 600A *dedicated PV* subpanel w/ (6) 100A circuit breakers, each
    feeding a 60kW inverter (72.2A rated output)
    - Subpanel is fused at 600A and connects to a larger main
    distribution/combiner panel along with other similarly configured subpanels

*Question*

    - Must the main panelboard be sized based on the combined total of OCPDs
    protecting the subpanels, e.g. 600A + 600A + 600A + 600A = 2400A main panel
    rating?
    - Or can the main panelboard be sized based on the combined total of
    inverter output ratings feeding the panel, e.g. 433.2A + 433.2A + 433.2A +
    433.2A = 1732.8A main panel rating?

--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to