Dan, you certainly can graph individual shunts in OpticsRE. They are located under the "Battery" tab, lower left from the main dashboard. By default, the shunts (i believe) are labeled A, B and C respectively, but you can name them anything you like. I suggest "Inverter" for A, "PV" for B and "Wind" for C. If you have the shunts wired correctly as per the FNDC manual, power through the shunts will add and subtract and net the correct values (as long as you are using the appropriate resistance shunts (and the sense wires are oriented in the correct polarity as per the manual). If you are using a backup AC generator and it is being utilized through the inverters charger, then shunt A will reflect the values in either direction (both charge and discharge, to and from the battery bank). Aside from calling Outback, you can catch me off list and I can explain. I also second Johns comment about the quality of internet connection, its quite important for Optics to get good data into the database, especially if you are writing any parameters to the equipment.
Roy Rakobitsch NABCEP Certified Small Wind Installer® Certified Advanced Tower Climbing, Safety & Rescue Wind/PV Design Engineer Windsine LLC 631-514-4166 www.windsine.org On Fri, Mar 16, 2018 at 9:43 PM, Dan Fink <[email protected]> wrote: > Esteemed Wrenches; > > We recently installed OpticsRE monitoring for an existing off-grid site in > Southern Colorado. It is 24v battery bank, 2.2kW PV, 2 Outback Flexmax 60 > controllers, nice old Trace SW inverter, and new wind turbine + controller > to replace a failed Whisper 200 with worn out furl and yaw bushings. > > We installed a FlexMaxDC shunt monitor into the Outback Hub, with the old > TriMetric shunt set as "inverter" and a new wind turbine shunt set as "wind" > > We removed the existing Bogart TriMetric and replaced it with the Mate 3s > and , everything is working fine for remote monitoring. But because the > Mate can't talk to the Trace inverter, it appears the PV input is > subtracting from the inverter output on that shunt. Thinking that moving > the PV input to the other side of the shunt will fix that, as the charge > controllers are talking to OpticsRE just fine. > > Questions: > > When the gasoline generator starts from low SOC (from the Trace SW relay) > will the FlexMaxDC Shunt A show a positive charging gain from the generator > or does FlexmaxDC only show one way (load or charge)? I don't see any way > of separating inverter load vs. generator gain. We will test this next > month down there, but it's 5 hours away, we just want to be prepared. > > Is there any way to graph the FlexMaxDC shunts on the main online > dashboard? They seem like a neglected child, only accessible by clicking > multiple menus, and just downloading data to a spreadsheet. The idea was to > show the client on a real-time graph how much the wind turbine is > contributing versus PV. > > For that main dashboard, we realize that without an Outback > inverter/charger, the graph will never show gasoline "generator" but if it > showed inverter loads as a gain, that would be enough. > > Still getting our heads wrapped around OpticsRE, but the setup and > commissioning was very easy, and it does work, after running a bunch of > CAT5 hardwired; Concrete/Adobe structure filled with remesh blocked all > efforts for wifi, The wifi router is located in the solar thermal room > downstairs (the ReSol monitoring works great on the thermal) and barely a > whiff of it upstairs at the electrical control room....OpticsRE seems to > need a pretty robust internet connection. > > Any thoughts appreciated, this is our first OpticsRE install. > > > > > Dan Fink > Professor of Solar Energy Technology, Ecotech Institute > IREC Certified Instructor™ for: > ~ PV Installation Professional > ~ Small Wind Installer > Executive Director, Buckville Energy > NABCEP Registered Continuing Education Providers™ > 970.672.4342 > > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org

