Corey,

I have been studying IR diagnostics quite a lot, but I haven't had a whole lot 
of opportunity to "get my hands dirty" with it, so I'm not sure how much help 
I'll be. I would like to know how many modules are in each string.

I'm going to share some random thoughts on this, but nothing here is at all 
conclusive, and if anyone can correct some flaws in my logic, I'd love to hear 
it!

It doesn't look like a simple, obvious problem. Your curve trace has a 
predicted Isc, with a dampening current to the knee, it has a sharp knee, then 
it has a low voltage at Vmp, and it stays really low all the way to Voc. A high 
series resistance would explain the dampening current to the knee, but it 
wouldn't explain the low voltage at all. If there was high resistance in the 
cells, you should see signs of diodes activating unless all of the cell groups 
had relatively uniform resistance.

Generally, the hot cells in the checkerboard pattern are underproducing 
compared to the cooler cells. Because they can't pass on as much current, they 
are actually wasting some of the energy that the other cells are producing. 
This wasted energy turns into heat. The often times, they waste more energy 
than they are producing themselves.


Alternatively, there could be other issues (or damage) at the hot cells.

The fact that the checkerboard pattern goes away when you shut off the inverter 
may be helpful. If you short out a module, it will almost always look like a 
checkerboard in an IR shot, and if a diode shorts out, that third of the module 
will generally look like a checkerboard.

This is the confusing part... Because the checkerboard appearance goes away, 
that would most likely indicate that it's not an issue of a short circuit 
failure (such as short-circuited diodes, or short-circuited modules). On the 
other hand, your curve trace looks somewhat like what you'd expect if you had 
some short-circuited diodes.

It looks like you have a calculated Voc of around ≈860, and a measured Voc of 
around ≈725. That's about 84%. My initial first guess based on this curve trace 
alone would have been that perhaps roughly 16% of the cell groups might be 
shorted out. So if you had 20 modules per string, that would be 30 cell groups 
(assuming 3 diodes per cell group). With these hypotheticals, you would have 
somewhere around 5 shorted cell groups.







Now that I'm looking at this closer, the knee of the curve is very quite sharp. 
I wonder if this could be caused by a higher resistance short somewhere out in 
the array (or in a conduit somewhere). (Perhaps this could be from compromised 
insulation or water intrusion somewhere??) Assuming that this isn't an 
intermittent problem, this would be easy to test under Voc. Just take a good DC 
amp clamp into the array while the inverter is shut down, and test the PV wires 
several places to try to find current in the array.

Under this hypothesis, as the curve tracer starts pulling current, and the 
measured voltage falls from Voc, it gets to a point where suddenly, the fault 
isn't passing as much current. This would cause the sharp knee on the curve 
trace. As the voltage gets lower, the current at the fault would also get lower 
and the measured curve would increasingly get closer to the predicted curve. 
This model would also explain why the checkerboard phenomenon goes away when 
you turn off the inverter... it would be because the current going across the 
fault would be much lower than Isc, so when it's resting, there isn't enough 
current flowing to produce the checkerboard effect. Using this hypothesis, the 
checkerboard phenomenon might not be indicating a problem in the modules at 
all. If there is a high resistance short somewhere in the array, then that 
would cause the actual current in the modules to be above the predicted Imp 
because the current is being lost before it gets to the inverter. Because 
nearly all modules get the checkerboard phenomenon at Isc, it wouldn't be 
surprising if many normal modules would also get the phenomenon if they're 
operating between Imp and Isc.



Again, take these thoughts with a grain of salt. If anyone sees somewhere that 
I'm going wrong, I'd love to hear from you! Hopefully, something here helps!

Thanks,
Kienan


Maxfield Solar
[email protected]<mailto:[email protected]>
(801) 477-0-SUN (477-0786)
(801) 631-5584 (Cell)
________________________________
From: RE-wrenches <[email protected]> on behalf of 
Corey Shalanski <[email protected]>
Sent: Thursday, May 17, 2018 4:19 PM
To: [email protected]
Subject: [RE-wrenches] PV Cell Temperature Variation

On a recent utility-scale PV installation we noticed a strange phenomenon on a 
single string on a single inverter. An IV curve (attached) reveals that the 
measured performance characteristics for this string (solid line) are 
significantly less than the expected values (dotted line). For reference, the 
ambient temperature was 31°C and the irradiance was 1010 W/m².

The phenomenon that more so caught our attention is apparent on a thermal image 
(also attached) of the modules in this string. For lack of a better term I 
would describe the distribution of cell temperatures as resembling a 
"checkerboard" or "scattershot" (random) pattern, ranging between roughly 55°C 
and 70°C. Interestingly this phenomenon was only apparent while the inverter 
was operating, i.e. with the inverter turned off the modules revert to a much 
more uniform temperature distribution nearer to 55°C, instead varying by only a 
couple degrees across the entire module/string.

There was no apparent physical damage to the modules.

Can anyone offer any suggestions about what might be causing this phenomenon?

--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to