I learned from Outback yesterday that an important step in using this RS initiator is not described in the directions. The prewired GFI needs to be removed and the conductors connected to their supplied RTB breaker that is supposed to be located in the same slot. The GFI function is inthe combiner box.

Has anyone found Outback instructions describing this?  The person I worked with on the phone yesterday could not find any directions to this effect.  Chris



On 7/25/2018 7:23 PM, Scot Arey wrote:
Yes I had also heard from Outback  that AC Coupling not supported.

Too bad because the AC coupling load center was slick setup and integration.

Scot

Get Outlook for Android <https://aka.ms/ghei36>




On Wed, Jul 25, 2018 at 10:29 AM -0600, "Kelly Keilwitz, Whidbey Sun & Wind" <[email protected] <mailto:[email protected]>> wrote:

    Larry,
    I recommend considering retrofitting the SolarEdge “StorEdge”
    Li-ion battery. It’s a high-voltage battery on the PV side of the
    inverter. We have a few out there now for a few months without a
    problem. Really like the design concept of the storage on the PV
    side, increasing system efficiency.

    We’ve done quite a few AC-coupled systems, which Outback FX,
    Outback Radian, and SMA Sunny Island/Sunny Boy. The Outbacks
    require a cutout relay. We won’t do Radian AC-coupling any more,
    as the setup, documentation, and support is a royal PITA, and have
    had failures in the “ROCB” automatic cutout breaker. Even when the
    ROCB doesn’t fail, it often cuts out when it isn’t supposed to,
    like at the start/end of a float cycle. My understanding is that
    Outback doesn’t support AC-coupling any more with the Radian.

    Kelly Keilwitz, P.E.
    Principal
    Whidbey Sun & Wind
    Renewable Energy Systems
    NABCEP PV Installation Professional
    WA Electrical Administrator
    office: 360.678.7131



    On Jul 19, 2018, at 07:07, Larry Brown <[email protected]
    <mailto:[email protected]>> wrote:

    Does anyone have a recommendation on a battery based inverter to
    AC Couple with a Solar Edge 11400A-US Inverter that is already
    installed?
    I have been working a lot with the Schneider Conergy XW+
    Inverters for off grid but have no experience AC Coupling them
    with a Solar Edge Inverter
    Any recommendations?

    Thanks
    Larry

    Larry Brown
    Sun Mountain
    845-657-8096
    [email protected] <mailto:[email protected]>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978

EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to