We’ve installed many Midnite BHs with the disconnecting combiners (and battery 
disco modules pre 2017 NEC.)
Recently we set up a roof mounted array with the disconnecting HV combiner 
along with the SOB for the PV Side of the CC. Worked well.
I’d be interested in the OB gear as well.


Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.

On Aug 14, 2018, at 5:45 PM, Ray <[email protected]<mailto:[email protected]>> 
wrote:

Hi All;

Its time to beat this poor dead horse again:  What is the latest, greatest ways 
to comply with 690.12 for lower voltage 150 Voc array with a charge controller 
in an off grid system?  At the moment, we are planning on using Midnite's new 
SOB system, and were told that while it won't work with most charge 
controllers, that it does work with Magnum's PT 100.  I'd like to hear from 
folks that have done this, any problems you've had, and also an explanation of 
why their transmitter is powered by 12 vdc, and not 24 or 48 vdc.    We 
definitely don't want to have the PV array dependent on AC power, so their AC 
transmitter is out.  If the inverters shut down from low battery voltage, the 
last thing we want is for the array to shut off too.

I've done a few Birdhouse setups and found them to be fatally flawed. If there 
is a nuisance trip, (seemingly relatively common) the customer had to scale the 
roof to reset the PV array to "ON". I'm also looking at Outback, but it seems 
prohibitively expensive.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to