I agree that the RSD requirements are too onerous and give the MI and MLPE 
players are leg up on string inverters with their add-on solutions.

 

Ditto for IFC requirements for a 3’ roof ridge setback. Still have not met a 
fire chief who says that venting is their method but when asked if they’d like 
to cede the space back by policy, the answer is, “no, why would we?”

 

Broadly speaking, energy efficiency measures mandated for “solar ready” are not 
enforced but the “safety” measure are. 

 

Probably time for an academic study figuring out the cost we have incurred in 
the pursuit of this, versus the risks avoided.  I know, I know…somebody is 
going to say, “if we’ve saved one roof fire…” But that mentality makes for a 
lot of costs, sometimes without much logical basis.

 

Scot Arey

Solar Centex

 

 

 

From: RE-wrenches <[email protected]> On Behalf Of 
[email protected]
Sent: Thursday, August 23, 2018 6:32 PM
To: RE-wrenches <[email protected]>
Cc: Rebecca Cantwell <[email protected]>
Subject: Re: [RE-wrenches] Rapid Shutdown Again?

 

I think Rapid Shutdown should be scrapped professionally and personally.  It 
was ill conceived and ill written.  Anyone willing to join me in a petition to 
CMP 44 and the like, contact me off list.  

To your question directly, you have a ground mounted system and you are not 
subject to 690.12 unless your conductors are "in or on building" which i cannot 
seem to find what that actually means. Exempted are buildings that are isolated 
only for the PV system This is a big win for installers as almost everyone 
installs systems like this.......   Right.    They used to have a dimension to 
this, but I guess that gave installers too much information. This is a stupid 
Code addition for roof mounted pv systems, disguised as protecting 
Firefighters, but not doing so in reality. The NEC looks politically 
compromised by consultants and manufacturers who too advantage of this fear 
mongering. No other country with a pv industry has historically done this. Why 
are installers not up in arms about this?

This is the NEC reference.

690.12 Rapid Shutdown of PV Systems on Buildings. PV system circuits installed 
on or in buildings shall include a rapid shutdown function to reduce shock 
hazard for emergency responders in accordance with 690.12(A) through (D).

If your system is ground mounted, you are outside the "altruistic" intent of 
690.12 of protecting Firefighters. Put a initiation device disconnect switch at 
the array.  Any supporters of RS should chime in with the support of 690.12 and 
add clarity and guidance to those of us who actually install systems and have 
to deal with this baloney.  690.12 has caused more problems for multimode 
systems than any tariffs, which are bad enough. I don' think the industry needs 
any more "safe design and installation" assistance from the CMPs involved with 
this issue.

Chris Warfel

 

 

 

 

 

 

On 2018-08-23 00:31, Ray wrote:

Greetings fellow wrenches;

I know we have beat this many times but I once again have not been able to 
resolve the contradictory information in 690 in regards to implementing 690.12. 
 As Rebekah Hren pointed out before, the diagrams shown in Figure 690.1(b) show 
that the PV System DC Circuit stops at the PV Disconnect.  Note 2 says 
specifically the 'PV Disconnect separates the PV system from all other 
systems'.  But then in the definitions in 690.2 on the next page, the new 
definition of a PV System DC Circuit says that it includes DC to DC converter 
output circuits.  (which are Solar Edge module level controls, but could be 
interpreted as a MPPT battery charge Controller?)  

Then 690.12 which only applies to 'PV System circuits in or on buildings', says 
we have to control conductors more than 3 ft after penetrating the building.  

So in my case, I'm looking at a ground mount, and installing an external 
lockable disconnect on the wall before it goes into the building.  This will 
officially be the PV Disconnect.  In my interpretation, I should not need to do 
any Rapid Shutdown, because I've essentially prevented the PV system from ever 
entering the building at all ( based on the 5th diagram and Note 2)  However, I 
could see an AHJ claiming I had to do RS all the way to the output side of the 
charge controller.

If this were true, could I simply apply RS equipment from the PV disconnect to 
the output of the charge controller, or am I back to module level shutdown for 
my ground mounted array, or could I build a tiny building that just housed the 
PV Disconnect and take the exemption for 'buildings with the sole purpose of 
housing PV system equipment'?  

Essentially the definitions in 690.2 are too broad, and are at odds with the 
Figure and Notes of 690.1.  They really didn't fix this in the 2017 code for us 
lowly off gridders. Charge controllers are covered by article 706.23 Charge 
Control, and NOT by 690.12 at all. IMHO, the charge controller needs to be 
clearly defined and differentiated from DC to DC converters like Solar Edge's 
module level DC equipment.  

I just want to go back to doing solar designs and installations, and quit 
acting like an attorney parsing every word of this confusing code language.

-- 
Ray Walters
Remote Solar
303 505-8760

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to