Ray is coming at this from an electricians viewpoint. He is correct if talking about wiring outside of a UL or ETL listed product.

The reason for wide radii in wiring is so the wires can be rerouted and terminated a few times.

8 times the diameter is a very large bend radii and would never fly inside a product, so why can a manufacturer do it?

Copper has the tendency to work harden when bending back and forth. That will damage the current carrying characteristics of a wire.

Bending a wire once does not work harden them. The insulation can get scrunched depending on the actual bend radii, but it is

only cosmetic after one tight bend. There are no actual cracks that would jeopardize the insulation integrity.

We have investigated this and determined it to be cosmetic in nature for a single bend. That said, I don’t like it either

because it makes installers nervous and doesn’t look good. The tight wire bends are no different from putting tight bends

on a sheet metal copper busbar. We do this all the time and always have. Testing shows that it does not constrict electrical flow.

If you straighten that same copper busbar and bend it again, it is likely to break in half. That is work hardening to the extreme. So, there is no violation from tight wire bending inside a listed box. A listed box does not have the same restrictions as the NEC.

Believe me, I too do not like zero radii bends and we have custom made pliers that give the wire a gradual radii, but that is cosmetics only.

The wire is not actually damaged unless you straighten it up and re-bend it. We do not do that!
Thanks,
Robin Gudgel
MidNite Solar



On 10/15/2018 11:27 AM, Will White wrote:
NEC doesn't apply to the interior components of a UL listed device although I do see your point. I'm assuming they designed it taking that bend into consideration.

On Mon, Oct 15, 2018 at 1:20 PM Ray <[email protected] <mailto:[email protected]>> wrote:

    Greetings;

    I've noticed several of the factory wired power panels over the
    years from Magnum, Outback, Midnite, Etc are not compliant with
    NEC 300.34 wire bending radius. (Radius should not be less than 8
    times the diameter) Basically they should look like sweep bends in
    PVC conduit, not plumbing.  Here's a pic from a recent Magnum system

    You can see the kinks in the insulation on the inside of the bend,
    and the color fading on the outside from being overstretched. 
    Some might think this is neat work, but its actually permanent
    wire damage and a code violation. Imagine the strain on the copper
    inside.

    Midnite is very proactive and has improved, I ask that Magnum do
    the same and soon.

    Thanks,

-- Ray Walters
    Remote Solar
    303 505-8760

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--
*Will White*
Curriculum Developer


e: [email protected] <mailto:[email protected]>
w: www.solarenergy.org <http://www.solarenergy.org/>
p: 802-272-3092

PV Installation Professional
# 093006-34

/FACT: If we covered 0.33% of the earth with solar panels, we could power the world with renewable energy./

Do you envision a world powered by renewable energy? Be the change <http://solarenergy.org/donate>.



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to