Is it possible that there was a lightning strike nearby, and the light
flash created the high max power readings? I'm calculating almost
1400 w/ m2, (3075/2205 x 1000 w/M2) which is high, but not insanely
high. They used to use flash testing to rate modules, so a fairly
instantaneous flash can do it.
Ray Walters
Remote Solar
303 505-8760
On 11/21/18 11:10 PM, [email protected] wrote:
Compadres,
I have 4 identical arrays of 3 strings of 3 Solarworld SW 245 mono
(2010 model) to FM80s. When designing, not exceeding 150 voc was
critical. No record temp data available. Location ~ 4,000' Pacific
Northwest. Recently replaced an FM80 with 6 blown FETs showing max
power at 3075 watts! This from a 2205 watt array into a 24 volt
battery. Max historical voc is ~120. My guess at record low temp is
-10F. tc%/ºC MPP doesn't get anywhere close. What would the WM2 need
to be in order to achieve 3075 watts on a 2205 watt array? BTW, 2 of
the four original chargers are still working fine and one of them also
shows 3075 watts max power. Edge of cloud effect against snow field at
bottom of array?
Cheers,
Bruce Fiero-RMI
*
*
*"*/*Energizing the Rogue Valley"*/
4115 S Pacific Hwy
*Medford, OR 97501*
*
*
*P:* 541.535.3965
*F:* 541.512.0061
*E:* [email protected] <mailto:[email protected]>
*W:* Willpower Electric, LLC <http://www.willpower-electric.com>
*CCB */191852/
*Oregon Electrical Contractor */C681/
**NABCEP*/**/*Certified Solar (PV) Installer *031409-38//*
*DUNS* /191470363/
*Energy Trust of Oregon Trade Ally */Solar (PV) Installation & Energy
Efficient Commercial Lighting Programs /
/
///
/**This email may contain information that is privileged,
confidential, or otherwise exempt from disclosure under applicable
law. If you are not the addressee, or if it appears that you have
received this email in error, please advise me immediately by reply
email, keep the contents confidential, and immediately delete the
message and any attachments from your system. /
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org