Hi Esteemed Wrenches,

Does anyone have an experience with using the BatFan relay function on the Sunny Island Relays?

I'm familiar with setting a voltage point for a relay to control a battery box fan but I'm unfamiliar with how the BatFan functions works.

The only setting I can find on the SI menus related to BatFan is battery temp.  But then elsewhere I read that the SI will turn on the fan anytime there is gassing.  Surely it can't be determining when it's gassing from only battery temp?

Or like in true SI fashion is there some complicated and thorough algorithm functioning that's is tracking the charge cycles and voltage? But no where to set those parameters?

Also - I've read through a few conflicting methedologies for calculating CFM needed for any given battery bank to clear the Hydrogen.

Zephyr says that there fans are designed for battery packs 2000 Amp-Hours or less charging at 150 Amps or less.

I have a largish off-grid system (18KW) with 2490 AH (20hr) of batts set to charge at 200 Amps max.

Should I be revisiting those calcs and see if I can find a definitive methodology or will using 2 48 Volt Zephyrs do the trick?

Thanks!

Jeff

--
Jeff Clearwater
Village Power Design
<http://www.visionarycommons.org>www.villagepowerdesign.com <http://www.villagepowerdesign.com>
Ecovillage Design Consultant
http://www.villagelab.net
New Paradigm Economics
http://www.visionarycommons.org
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to