Mike:

Ac input is 207 Vac at 60.00. Display says unit configured for 208.

I have been talking to tech support for days. They say my voltage is low. That 
disagrees with the manual and the name plate sticker.

A bit frustrating...  I bid the job and I can’t bill until this is sorted. Ah, 
the joys of being one’s own boss. 

Thanks for your help. 

William

> On Apr 23, 2019, at 12:21 PM, Harry Mahon <[email protected]> 
> wrote:
> 
> William - yes, waiting is usually waiting for grid to come back within spec 
> or for DC voltage to get to start.  260 should be plenty.  208V with neutral 
> should be fine without adjusting the jumpers.  Have you measured the AC 
> voltage at the inverter terminals?
>  
> May want to contact service for this one.  1-877-697-6283.
>  
> Best regards –
> Mike
>  
> From: William Miller <[email protected]> 
> Sent: Tuesday, April 23, 2019 12:40 PM
> To: Harry Mahon <[email protected]>
> Cc: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] SMA Micro-grid
>  
> Mike:
>  
> Thanks for the reply. Good information. 
>  
> The AC system is 208. The data sheet indicates that for 208 the PV startup is 
> 220. Today we have 260 VDC. That should be enough!?
>  
> I checked EMT he AC frequency in case it was on shift mode. It is right at 
> 60.00. 
>  
> Still in waiting mode. I had always thought “waiting” was for grid reconnect 
> timeout...
>  
> William
> 
> On Apr 23, 2019, at 8:47 AM, Harry Mahon <[email protected]> 
> wrote:
> 
> William –
> Waiting mode means the DC voltage is below the inverter start.  For SB 
> 4000-12, that would be 285 VDC (and will work to 250VDC once that is hit).
>  
> If you knock on the inverter lid, the display will cycle and you will see the 
> DC voltage displayed.
>  
> If the yellow LED is not on, this should not be an AC side issue.
>  
> I do not think the “Backup Mode” parameter would be the cause, but if the 
> voltage check shows well above PVstart, it would be worth a call to service.  
> If the inverter was left in on grid mode, then it will work when the SI is 
> creating a micro-grid with frequency within UL1741 limits.  If the system is 
> off-grid, I would think the SB would have been set to off-grid mode rather 
> than enabling Backup Mode to “on all” that allows switching from on-grid to 
> off-grid parameter sets by RS485 command.
>  
> Best-
> Mike
>  
> From: RE-wrenches <[email protected]> On Behalf Of 
> William Miller
> Sent: Monday, April 22, 2019 6:54 PM
> To: RE-wrenches <[email protected]>
> Subject: [RE-wrenches] SMA Micro-grid
>  
> Friends:
>  
> I am working on an AC coupled SMA system in an off-grid setting.  We have an 
> SB4000-12 that was disconnected for a number of years and we reconnected it.  
> The inverter is stuck in the waiting mode and  will not generate power.  The 
> Sunny Islands and Sunny Boys are connected via an RS485 communication system.
>  
> I suspect there is a programming step I have not yet accomplished.  I recall 
> some years ago I programmed the other Sunny Boys for off-grid operation.  I 
> can’t find anything in any of the manuals about how to check the programming. 
>  I also suspect SAM tech support talked me through this and the information 
> may not be published.
>  
> Does this ring a bell with any of you?  Any advice? 
>  
> Thanks in advance.
>  
> William Miller
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com
> CA Lic. 773985
>  
> Quote of the day:  “If there is a job you hate, get really,
> really good at it. Maybe you will hate it less.“ W. Miller
>  
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to