Hi Wrenches, Does anyone have a recommendation for a meter main with a 225A bus and pass through lugs? Eaton and SquareD make meter mains with a 225A bus, but no pass-through lugs, so they don't work well for most retrofit applications.
We would like to connect our inverter output to a feeder that is fed by the pass through lugs in the existing 200A meter main (which is located at another building.) The inverter output has a 60A OCPD, so the 200A meter main bus is not sufficient. Any suggestions you have would be greatly appreciated! Thank you, Sarah Ray OnSite Energy, Inc. 619 N Church Ave, Suite 4 Bozeman, MT 59715 Cell: (406) 579-6512
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org