You’re losing about a third of your voltage so one cell bank is out of the 
circuit. Either a shorted closed diode (more likely IMHO) or fully open 
connections somewhere in a cell bank (probably visible if between cells, if in 
the jbox, well it depends on the jbox). 

If you short circuit the module, or connect it to a load, and with enough 
irradiance, you should be able to see the diode heat up with an IR camera or 
maybe even locate it - or the associated cell bank, which will also be hotter 
than the two good ones - with another type of temperature sensor. 

If you can access the diode and isolate it, most DMMs have a diode year 
function. 

Brian

> On Jun 11, 2019, at 2:38 PM, Drake <[email protected]> 
> wrote:
> 
> Hello Wrenches,
> 
> Would you expect a low open circuit voltage in a module to be due to a 
> problem in the J-box / diodes or the module itself? The OC voltage read about 
> 28.3 V, where as the STC OC voltage of the module is 37.3. 
> 
> The module is an LDK 240, which means no warranty. 
> 
> Thanks,
> 
> Drake 
> 
> Drake Chamberlin
> Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV 
> 740-448-7328
> http://athens-electric.com/ 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to