Are you required to meet the latest code?  In many retrofit/ replacement situations, you are only required to meet the code requirements of the date the original system was installed.  Metal vs PVC is dependent on the code version you are meeting.  Was metal a NEC 2008 requirement? I don't have my old code versions here.   When metal is required, its only from the point of entry into the building to the inverter, so if you mount the inverter outdoors, it doesn't have to change either.  I've got lots of legacy systems that have PVC  on the inside, and never had an issue.  Seems like more trouble to change out than its worth, but if the AHJ requires it, then yes.

Also, you didn't mention if the array was roof or ground mounted, which would effect the 690.12 interpretation.

Ray Walters
Remote Solar
303 505-8760

On 6/12/19 12:49 PM, Kirk Herander wrote:

All,

I am retrofitting an existing PV system with Storedge / LG Chem / optimizers and updating some code issues. I am replacing the PVC conduit carrying the array conductors into the building with metallic raceway to the point of DC disconnect(i.e. the inverter).  The array is presently connected to an Outback inverter / FM60 controller / AGM batteries (grid tied with backup). If I am interpreting NEC 690.12 etc. correctly, a DC disconnect outdoors is generally not required because of new rapid shutdown capability, amongst other reasons. Would this be the case regardless of metal or plastic conduit penetrating the building? The system at present has no outdoor DC disco, and to me that’s a violation in addition to lack of metallic raceway entering the building. Thanks.

*Kirk Herander*

*Owner|Principal, VT Solar, LLC *

*/Celebrating our 28^th Anniversary 1991-2019/*

*www.vermontsolarnow.com <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>*

dba Vermont Solar Engineering

NABCEP^TM 2003 Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to