Hello Wrenches,

I'm working with a small utility on a large residence for grid-tie solar
with a wind-turbine.  They have a 25 kW backfeed limit.  Its a 4 stack
radian system with about 25 kW of solar and 10 kW of wind.  The wind is AC
coupled Bergey and the solar is DC coupled with FM100s.  My idea was to use
the Radians to limit the solar to 15 kW and let the wind do its thing.
However, the utility doesn't like the idea that this limit could be changed
without their knowledge.

Has anyone designed and/or implemented a backfeed limiting circuit that
could knock some charge controllers off-line in case that 25 kW limit is
reached.  Is there anything off-the-shelf that can do that?

Thanks in advance

-- 