I was just reminded that  exeltech can do up to 125kw. 

Jay 






> On Jul 21, 2019, at 3:05 AM, Tump <[email protected]> wrote:
> 
> Victron has the Quattro 10kW inverters w/ 100A pass thru and they have a good 
> battery management for their Li battery line. They have also started to have 
> their products UL listed. GOOD robust product and good support. Allen 
> formerly of Magnum is cc ed here.
> Up to 6 Quattro units can operate in parallel. Six units 48/10000/140, for 
> example, will provide 48kW / 60kVA output power and 840 Amps charging 
> capacity. 
> 
>> On Jul 20, 2019, at 5:13 PM, Mac Lewis <[email protected]> wrote:
>> 
>> I think Outback is the only major inverter manufacturer that can do split 
>> phase 120/240 to that size.  You have to go 3 phase for 36 kW continuous 
>> capacity with either Schneider or SMA.
>> 
>> Good luck, sounds like a fun system to design.
>> 
>>> On Sat, Jul 20, 2019 at 2:50 PM Lou Russo <[email protected]> 
>>> wrote:
>>> Blue Ion 2.0 with Outback or SMA. Works every time. 
>>> Blue Planet's tech support is great, the warranty is even better. 
>>> 
>>> Aloha,
>>> 
>>> Lou Russo
>>> [email protected]
>>> 808 345 6762
>>> Spree Solar Systems LLC 
>>> CT-34322
>>> 
>>> 
>>> 
>>>> On Sat, Jul 20, 2019 at 10:36 AM Jay <[email protected]> wrote:
>>>> Hi Marco,
>>>> 
>>>> Is the max surge 7kw, which is what is listed on line?
>>>> 
>>>> Jay
>>>> Peltz Power
>>>> 
>>>>> On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf <[email protected]> 
>>>>> wrote:
>>>>> 
>>>>> Seven to eight Tesla Powerwalls will get you that assuming that the 
>>>>> service entrance is no bigger than 200A.
>>>>> 
>>>>> marco 
>>>>> 
>>>>>> On Friday, July 19, 2019, Jason Szumlanski 
>>>>>> <[email protected]> wrote:
>>>>>> What are current popular options for battery based systems in the 100kWh 
>>>>>> range? Preferably Lithium.
>>>>>> 
>>>>>> Also, what inverter pairing is suggested with total stacked capacity of 
>>>>>> 36kW, 120/240V?
>>>>>> 
>>>>>> This is slightly larger than some of the systems I have worked with 
>>>>>> recently. I'm a bit out of the loop, particularly on the battery side of 
>>>>>> things.
>>>>>> 
>>>>>> Jason Szumlanski
>>>>>> Florida Solar Design Group
>>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: [email protected]
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: [email protected]
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
>> [email protected]               www.SWNL.net
>>                 Solarwinds Northernlights       
>>        Serving Mid Coast Maine & Northern California
>>                          207-832-7574   Cl. 610-517-8401                     
>>          
>>                               Blair "TUMP" May
>>                ********  MAINE'S CHARTER ********
>>                       NABCEP    "Certified PV Installer" 
>>    
>>               ********  MAINE'S CHARTER ********
>>                   Trace Xantrex "Certified" Dealer / Installer"
>> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to