Hey There Wrenches,

So be advised that after a little research the SW dual stack will NOT double the surge ratings of a single SW.

But that brings me to my second question:

What inverter surge rating should one refer to when looking at maximum Inrush or LRA - 1ms? 100ms?  1 sec?

Yourengineering wisdom welcomed!

Thanks,

Jeff



Jeff Clearwater wrote on 7/23/19 8:27 PM:

Thanks for the tip! I'll check the firmware.

Dave Angelini Offgrid Solar wrote on 7/22/19 9:11 AM:

Hi Jeff,

I am not going to guess if this will work, it should.  I use XW's because they start anything I have come across.

If you do this, make sure but SW's have the latest and same firmware. There were problems with stacked SW's early on in their development.

*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail [email protected] <mailto:[email protected]> text 209 813 0060*

On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater <[email protected]> wrote:

Hey Esteemed Wrenches,

So I recently built a power trailer with a single 4 KW (4048) Schneider SW for a client with a moderate cabin lifestyle.

But he lives on a high hill and even though his 2 HP Macerator is only rated at 15 amps continuous that baby starts up with a whopping kick - probably close to or at it's 53 Amps Locked Rotor rating.

The SW has the following surge capability:

SW 4048 Rated@ 240 Volts:
Continuous - 15.2 Amps 3700 Watts
30 Minutes - 18.3 Amps 4400 Watts
5 Secs - 29.2 Amps 7000 Watts
Max (100ms?) - 41 Amps - 9840 Watts

Can I be confidant that 2 stacked SWs will start this baby?

Any experience with similar macerators - or simply educated guesses?

Thanks!

Jeff

--
*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail [email protected] <mailto:[email protected]> text 209 813 0060*



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to