Howard - Some information related to your questions:

Yes, with AC coupling the output of the Sunny Boy Storage 6.0  (6.0kW) plus PV 
system is available.  For example, 13.7kW with SBS 6.0 at full output and Sunny 
Boy 7.7 also at full output (obviously daytime).  With 3 of the BYD Battery Box 
 10kWh units, SBS system scales up to slightly more than 30kWh usable storage.  
Yes, understanding and planning to customers loads is very important and will 
determine the customer's happiness with their system. The 50A breaker for PV on 
the ABU is appropriate for 40A continuous, or 240Vx40A = 9,600W.  The PV can be 
attached via breaker in protected loads panel downstream, but to ensure the SBS 
can throttle the PV production rapidly enough when offgrid, there still IS a PV 
size limit. If considering having more than 9.6kW of PV, please contact SMA 
Applications Engineering group.

When offgrid, the Sunny Boy Storage uses Frequency Shift Power Control (FSPC, 
like the Sunny Island). Some newer inverters will have Freq-Watt features 
enabled, "older" inverters will stop exporting power when frequency goes above 
60.5Hz.  Best to check with manufacturer on how any non-SMA inverter will 
respond - throttle or turn off.  The datasheet is showing a Sunny Boy with the 
hardwire communications as this provides for faster transition/smoother 
throttling and also supports the zero-export (grid-tied) use case.  For zero 
export, the SBS cannot adjust frequency and it requires a communication signal 
to control the PV power.  This requires a current Sunny Boy (likely possible 
with TL-US-22 as well, but I have not seen an example of this).

Feel free to contact me at 
[email protected]<mailto:[email protected]> for any more 
information.

Best regards - Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html

From: RE-wrenches <[email protected]> On Behalf Of 
Howard Arey
Sent: Friday, August 9, 2019 12:37 PM
To: 'RE-wrenches' <[email protected]>
Subject: [RE-wrenches] Anyone try the new SMA battery inverter with Automatic 
Backup Unit? Couple of questions.

Excited to use this and even more excited that one of our sales reps with a SMA 
system has offered to be our guinea pig!

The ABU looks great - just got one to the shop today - it has transfer switch 
with full 200A capability, auto-transformer, easy inputs for BB-inverter, PV 
inverter, and smart meter with CTs built for smart energy management.

Couple of questions for those that might know, but does the AC coupling of the 
PV inverter plus the 6.0 BB-inverter mean I might possibly push their combined 
full output to downstream loads. Even though 200-amp capable ABU, hard to see 
how I do whole-house backup. We think we get to "inside the walls backup only" 
which is good except during middle of summer. A bit more than StorEdge power 
output.

Does anyone know the protocol for decreasing the output of the PV inverter when 
batteries are full? I think it is freq shifting but the diagram does show 
communication via the home router between the PV inverter and the BB-inverter. 
I'd think if this was a necessary communication, then SMA would have insisted 
on a hard-wire connection. Any ideas on what might be shared and for what 
purpose.

This also leads to last question and if freq shifting is the mechanism for 
throttling back PV inverter output, then I'm thinking that using any brand 
inverter would work.

Look forward to answers and to sharing more as I put this at the home of our 
Guinea pig...I means sales rep!

Howard "Scot" Arey
Owner, Solar CenTex
NABCEP Certified PV Installation Professional
254-300-1228
[email protected]<mailto:[email protected]>

www.solarcentex.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.solarcentex.com%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C2037295dc7804d9fbbb708d71d15aa92%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637009851219123536&sdata=FxGIfqoFtmVagy75G2Xftc4EgagEqSsBRepeodZjaO0%3D&reserved=0>
https://www.facebook.com/SolarCentex<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FSolarCentex&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C2037295dc7804d9fbbb708d71d15aa92%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637009851219133529&sdata=vW1YaZJlp56RMdYdF%2BXWiQmrpxhA%2FLcbBoGQElA7CAM%3D&reserved=0>
Top-Rated Solar Installer in Texas by Solar 
Reviews<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.solarreviews.com%2Finstallers%2Fsolar-centex-reviews%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C2037295dc7804d9fbbb708d71d15aa92%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C1%7C637009851219133529&sdata=kpYnNxMsVCETyyZ0gYlvkn7LH%2Bco6MqOgmt6SOp%2BiwQ%3D&reserved=0>
[Solar Centex Logo - No Back]

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to