Hi Dan, Sorry for the confusion.

Maybe an example would help.  Take a 2000 w dc multimode system that is coupled with a 3600 w ac rated multimode inverter.  What percentage of the dc capacity is inverted into ac capacity.  So, roughly 2000 x .9 (wiring and similar losses from array to battery) x .95 for an assumed 5% usage to charge/float the batteries x .98 for dc to ac inverter efficiency makes me think that 2000 x .9 x .95 x .98 * (4.5 x 365) yields = 2,752 kWh annually. The utility is assuming roughly 3600 x .98 x (4.5 x 365) {if they are assuming anything at all} = 5,368 kWh revenue lost. The regulatory assumption overestimates the capacity factor by @49%.

I'll post to the WRENCHES too to help clarify hopefully.   Chris

On 8/28/2019 9:10 AM, Dan Lepinski, P.E. wrote:
OFF-LINE REPLY

Hello Chris,

The wording of your question is confusing.  You ask about the percentage of DC 
capacity vs AC power output, then add batteries into the mix.

What system topology is the focus of your query?

I'll be glad to do what I can to assist.  Just need clear direction on the 
configuration.


Regards,


Dan

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to