Esteemed Wrenches,
So from my previous post and research - I think I'm down to the simple
question of what is the best way to do a supply side connection in PG&E
territory for a 200 AMP PV feed into a 200 Amp Service.
PG&E won't allow PV circuit wiring to enter their sealed sections.
So how about a simple J-Box like this after a standard 200 Amp Meter
Socket box?
https://www.ideadigitalcontent.com/files/11028/784572230569_SS.pdf
Then it simply branches to a fusible 200 AMP disconnect for the PV side
and the other to a standard 200 Amp panel box for the house loads.
I'm feeding 5 SB7.7s so 160 Amps of rated PV x 1.25 = 200 Amps. right
at the limit but fully in code and PG&E compliance from what I can tell.
Anything I'm not thinking of? Easier way to do that "T" connection?
Existing equipment for 2 200 Amp Breakers off of a single 200 Amp service?
Thanks!
Jeff
Jeff Clearwater wrote on 10/21/19 11:51 AM:
Hey August, Jay, and Burt and all,
Thanks for the great input! and I'm sorry if I wasn't clearer.
They are not asking for 400 Amps - I suggested it as that was the
rating of the solar ready panel I specified.
They are just saying IF it's 400 Amps then they need room for CTs
cause it's a shop and hence residential equipment is not approved.
So as August and Glenn indicate below - perhaps the easiest is a 200
AMP meter can with a Supply side line. That does throw it back to my
AJH to approve but that is pretty standardI would hope. It also
requires the variance letter from PG&E.
I'm running 5 SB7.7s at 32 Amps each - so 160 AMPS of solar input.
So If I supply a 200 A meter can with supply side lugs that I can feed
into a 200 A fused disconnect and solar distribution panel and keep
the existing 200 Amp panel box fed by the 200 Amp main breaker - any
reason that won't work?
OR does anyone know of a commercial 400 AMP solar ready meter base
with 2 200 Amp feeds - one for solar and one for loads that does allow
room for CTs?
Thanks,
Jeff
August Goers wrote on 10/17/19 4:35 PM:
Hi Jeff -
PG&E defines the service rating amperage based on the enclosure
rating of the first piece of equipment the service hits. See section
1.14 in the Greenbook:
https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf
This might be why they insist that you need a 400 A service just
because you want a 400 A rated bus. The easy way around it is to
supply a 200 A rated meter socket and main disconnect, then feed a
400 A sub panel.
A meter/main like the Eaton MBEB200BTS might also work for you:
https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147
August
Luminalt
Hi Jeff,
Seems to me if allowed in your jurisdiction, you might be best served
by installing a new 200A fused service disconnect ahead of the
existing main service panel. Or even a 400A one to allow for
additional work inside (CT’s), then perform a supply side connection
in it. Some manufacturers of switchgear have an option for lugs that
accept multiple conductors, so no piercing of conductors needs to happen.
Good luck,
Glenn
On Thu, Oct 17, 2019 at 12:19 PM Jeff Clearwater
<[email protected] <mailto:[email protected]>>
wrote:
Esteemed Wrenches,
I am in need of changing out an existing 200 Amp service entrance
in order to accommodate a bus capable of handling a a 200 Amp
Solar backfeed (41 KW system) .
PG&E is upgrading the transformer to handle the backfeed but when
I proposed a Siemens SolarReady 400 Amp service entrance they
couldn't approve it cause since the building is a shop - they
classify it as commercial and require a panel that can handle CTs
when there is a 400 Amp service involved.
Anyone else faced with this have solutions? What is the cheapest
equipment I can provide to satisfy all requirements?
We don't need to upgrade the existing 200 amp service entrance
equipment for load purposes - only to meet the bus requirements
of backfeed.
Would it be cheaper and easier to use the existing (or new) 200
Amp residential panel - not call it a 400 Amp upgrade but simply
add a 200 Amp Supply Side Connection? Suggested equipment to do
that in the most economical manner?
Any help well appreciated!
Jeff
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org