Jason,
The Conext XW+ in grid support, either grid support sell or self-consumption 
and during solar hours. The inverter operates in parallel with the grid but 
prioritizes renewable energy.
At the end of the day, the inverter will decide which mode to switch next based 
on the battery voltage.
Since in most cases the batteries are in reserve for a power outage, the 
inverter will go into passthrough mode.
In passthrough mode the inverter support 100% of the loads utilizing power from 
the source (grid).
In some cases, it is possible that inverter may be required to also charge 
batteries from the source provided that the charger inside the inverter is 
enabled, then the inverter will enter into charging while still supporting 100% 
of the loads with the source, this is not common, since it is preferable to 
only charge batteries with the array.
Additionally, the Conext XW+ is not a power conditioning device, which means 
that it will not clean the source, the passthrough power quality that the loads 
will see is the quality of the source.

Sandra Herrera
[email protected]



From: RE-wrenches <[email protected]> On Behalf Of 
Jason Szumlanski
Sent: Friday, November 1, 2019 5:16 AM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Conext Inverter Grid Support Mode


[External email: Use caution with links and attachments]

________________________________


When the inverter is using this mode, at night or when there is not much PV 
power, are the laods seeing inverter output power or does the grid pass through 
the inverter, as in bypass the inverter directly to the loads. The manual says:

"In the morning, the PV system begins 3-stage charging of the batteries at bulk
stage and power from the grid passes through the XW+ (including XW) to the
loads."

That is not really clear. What does "passes through" mean? Does that mean the 
grid charges the batteries with the integrated charger simultaneously with the 
inverter outputting AC power, or does that mean the utility power bypasses the 
inverter and powers the loads directly while the PV system gets the batteries 
charged up?



While on the subject, and I don't think this is possible, but I have a Conext 
off-grid client that wants to have "clean" inverter power all the time rather 
than the generator power bypassing the inverters and powering the loads 
directly during battery charging. I told him it is not possible without using 
an external battery charger and eliminating the generator AC input to the 
inverter. I think I am correct on that, but I'll take any suggestions!


Jason Szumlanski

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to