A bit off topic, BUT testing equipment from these folks is a really great way 
to go;www.trsrentelco.com <http://www.trsrentelco.com/>. GREAT, PROMPT, cost 
effective tool rental and service. I rent the Fluke 1735 or the 1738 power 
logger for a month its under $300.00
> On Jan 23, 2020, at 3:16 PM, William Miller <[email protected]> wrote:
> 
> Colleagues:
>  
> In a recent post about some AC GFI tripping problems, I mentioned I am 
> measuring some high THD readings in certain scenarios—the highest being when 
> the generator is charging at high percentages:
>  
> Inverter only: 2.5% THD
> Gen Max: 19% THD
> Gen 5 Amps: 8% THD
>  
> I measured the THD using a Fluke VR1710 <x-msg://22/TJ3fTpspG2DGCzC>.  This 
> is a handy little gizmo and pretty expensive considering its size.  The 
> device has limitations:
> 1.   It is cord connected.
> 2.   Results cannot be viewed in real-time.
> 3.   It measures voltage parameters only.
>  
> Here are my questions:
>  
> 1.   Has anyone here had to consider problems with high THD in any off-grid 
> scenarios?
> 2.   What readings are normal?
> 3.   What is the significance of voltage harmonics versus current harmonics?
> 4.   What instruments are you using to measure THD?
> 5.   Has anyone seen high THD causing AC GFI tripping?
> 6.   What other symptoms might occur with high THD?
>  
> Tip: The reason we first started suspecting high THD is that cheap voltmeters 
> registered abnormally high (including the onboard Radian metering) during 
> periods of high THD, while true RMS meters (Fluke 87) continued to measure 
> normal AC voltages.  If you experience this situation, high THD is suspect.
>  
> Answers are always gratefully appreciated.
>  
> William Miller
>  
> PS:  If you are receiving a BCC of this email, it is because you are part of 
> the team working on this problem.  The message is directed to an industry 
> forum in hopes of gleaning additional knowledge.  I will share any results I 
> receive.
>  
> Wm
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> [email protected] 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to