Just to be clear the 8-pin RJ 45 cables are not Ethernet. They are Xanbus which 
is a version of Canbus, a type of serial communication. 

I’ve had some trouble shooting of Xanbus where the AGS was intermittent. I 
happen to have just finished a Radian job and had a bunch of green cables with 
me. I used those to replace the white cables and never had a problem 
afterwards. In other cases, I  have also made custom cables some very short and 
I made sure to terminate the last Xanbus connection and I usually use a long 
wound up cable at the termination point. 

I also started putting silicone jelly on all connections and that seems to help 
with longevity. 

A Canbus protocol analyzer or maybe an active Ethernet tester could help 
investigate extra difficulty. 

Good luck! 

Maverick


> On Jan 31, 2020, at 12:19 PM, Jeff Clearwater <[email protected]> 
> wrote:
> 
>  Hi Mac and William,
> 
> This is interesting because I was having an issue of the Xanbus network not 
> seeing the Battery Monitor until I replaced an ethernet cable.  My present 
> theory is that the white ethernet cables being supplied by Schnieder are 
> marginal.  
> 
> Given that many of our systems locate the monitoring components close to the 
> main battery DC Inverter cables and that the EMF noisy PV charge controls 
> with their medium voltage DC are also nearby -  especially going through the 
> tight quarters of a MidNite E-panel or equivalent - it strikes me that 
> inductive currents or EMF noise could be the culprit.
> 
> I'm wondering if for future installs I should just make up my own cables from 
> shielded CAT6 as a standard practice for all ethernet-based comm systems?  
> That said I've never had a problem with SMA - only Schnieder.
> 
> Thoughts?
> 
> Best,
> 
> Jeff
> 
> William Miller wrote on 1/31/20 8:15 AM:
>> Mac:
>>  
>> 1.   We have had this issue for years.  Specifically this affects AGS units. 
>>  We were told that bus cables had to be a minimum of 6’ to avoid “ringing.”  
>> Later (after we purchased and replaced cables) we were told there was no 
>> foundation for this claim.
>> 2.   Some Fluke advanced testers we have looked at have a “bus health” test 
>> function.  I think this is in the 125B Scope Meter and I see reference to 
>> the function with a BHT190 break out adapter.  The literature indicates 
>> applications on the following bus architectures:  Profibus, Foundation, 
>> Modbus, CAN-bus, AS-i bus and RS-485.  I will leave it to you to research if 
>> this function would be helpful.   BTW, the Scopemeter is about $3K and hard 
>> to get in a hurry.  You could probably rent one.
>>  
>> I wish you good luck in resolving your issue.
>>  
>> William
>>  
>> Miller Solar
>> 17395 Oak Road, Atascadero, CA 93422
>> 805-438-5600
>> www.millersolar.com
>> CA Lic. 773985
>>  
>> From: RE-wrenches [mailto:[email protected]] On 
>> Behalf Of Mac Lewis
>> Sent: Friday, January 31, 2020 6:19 AM
>> To: RE-wrenches
>> Subject: [RE-wrenches] Troubleshooting Xanbus
>>  
>> Hi Wrenches,
>>  
>> Does anyone have a good way to locate intermittent Xanbus issues with 
>> Schneider equipment?  We have a site that has been giving us a lot of 
>> issues.  It seems like the AGS might be dropping in and out and defaulting 
>> to "Off".  It works flawlessly when we are there of course.  Cables are 
>> testing fine.  No other device seems to have these issues.  All of these 
>> cables are factory made.
>>  
>> Maybe there is another explanation for the AGS defaulting to "Off".
>>  
>> Thanks in advance for your help
>>  
>> --
>>  
>>  
>>  
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> -- 
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin 
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to