Hey Jay,

Why not just use 8 SMA SB 7.7's = 61.6 KW rated, 32 Amps 240 each.

Then use a dedicated 320 Amp Rated (Typical nominal bus of a 400 A panel) Supply Side fed Breaker panel as you'll have 256 x 1.25 Amps of Solar bus = 320 - right at the limit but you are good to go!

Jeff



Chris Sparadeo wrote on 2/8/20 7:42 PM:
Jay,

Sorry, I missed the 120/240v part. That CPS product is 3 phase. Fronius has the Primo 15kW in split phase. Have had good luck with them.

On Sat, Feb 8, 2020 at 10:30 PM Chris Sparadeo <[email protected] <mailto:[email protected]>> wrote:

    Hi Jay,

    CPS has a 60 kW -1000v string inverter that might be a good fit
    for your project.

    https://www.chintpowersystems.com/commercial-60kw.shtml


    Best,

    Chris

    On Sat, Feb 8, 2020 at 8:54 PM jay <[email protected]
    <mailto:[email protected]>> wrote:

        HI All,

        I’m wondering what the largest GT battery less inverter  (and
        what people recommend) for 240v 60hz is out there.

        I don’t need MLPE, as project would be ground mount, its large
        residential, potentially 60KW.

        SE has their 11.4KW, but I’ve heard lots of bad things about
        them recently.
        Fronius has a 10KW?

        Thanks in advance


        jay

        Peltz power


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>

-- Chris Sparadeo


    C_802-369-4458
    H_802-728-3059

--
Chris Sparadeo


C_802-369-4458
H_802-728-3059


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to