Yes Sonoma county requires 30' minimum from ground arrays for fire
setbacks. and by extension 30' from property lines (as an array owner
can't control a neighbors brush removal) More is surely advised! I
imagine other CA counties have similar requirements.
Dave Angelini Offgrid Solar wrote on 3/20/20 5:32 PM:
In our area of California, when the green grass dies and turns brown,
the area under any type of array needs to be free of grass. An array
could ignite a wildfire if the array were emit sparks. This is a very
rare condition but it can happen to even the best design and module type.
There would not be any brush anywhere near an array. 10 feet from any
point of the array makes sense but if there were a wildfire I would
want alot more. 100 feet is typical for the zone around a home. That
is what our AHJ wants to see in an inspection. We are in a very
dangerous area for wildfires in the southern Sierra.
Brush does not count as grass. An array should survive a grass fire.
Brush would be much more dangerous and must be kept clear as it is a
much larger heat source than grass. I hope this is helpful.
*Dave Angelini Offgrid Solar "we go where powerlines don't"
http://members.sti.net/offgridsolar/ e-mail [email protected]
<mailto:[email protected]> text 209 813 0060*
On Fri, 20 Mar 2020 17:06:01 -0600, Dan Fink <[email protected]> wrote:
Hello esteemed Wrenches; I am trying to clear this up for a client
and his AHJ, which is also puzzled at how to interpret IFC 2018,
Section 1204.4, which states:
Setback requirements shall not apply to ground-mounted,
free-standing photovoltaic arrays. A clear, brush-free area of 10
feet (3048 mm) shall be required for ground-mounted photovoltaic
arrays.
I found one lone informational note in a white paper stating this was
to prevent a burning PV array from igniting surrounding vegetation
and the fire spreading.
So, has anyone dealt with an AHJ on this before? Our questions are:
* What exactly is a "free-standing photovoltaic array" that is
exempt? A pole mount? Couldn't burning debris from that ignite
vegetation underneath?
* What exactly does "A clear, brush-free area of 10 feet (3048 mm)"
mean? "10 feet" is a linear measurement, not an area, that would
be in square feet.
* What is "brush"? Does grass count as brush?
I would interpret this on the safe side as meaning that all
vegetation under the PV array and out to a 10 foot perimeter should
be cleared, except for pole-mount arrays (that exception makes no
sense to me).
I always recommend to clients that the area /under/ the ground mount
array should be pea gravel bordered by railroad ties, but out to 10
feet from the array edge seems excessive.
Any input greatly appreciated!
Dan Fink
Executive Director, Buckville Energy Consulting
NABCEP PV Associate
NABCEP Certified PV System Inspector
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP Registered Continuing Education Providers
d <mailto:[email protected]>[email protected]
<mailto:[email protected]>
970-672-4342
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org