Hey Wrenchers,
Wondering what you all think about NEC Article 705.95 and if downsizing the 
Neutral is common practice.   If your JHA accepts it and the model inverter you 
are installing complies do you see any issues with downsizing the Neutral?  
This section of code has been in place since 2011 and I must admit I have been 
slow to adopt it.

705.95 Ampacity of Neutral Conductor. The ampacity of the neutral conductors 
shall comply with either (A) or (B)
(A) Neutral Conductor for Single Phase, 2-Wire In- verter Output. If a 
single-phase, 2-wire inverter output is connected to the neutral and one 
ungrounded conductor (only) of a 3-wire system or of a 3-phase, 4-wire, wye- 
connected system, the maximum load connected between the neutral and any one 
ungrounded conductor plus the inverter output rating shall not exceed the 
ampacity of the neutral conductor.

(B) Neutral Conductor for Instrumentation, Voltage Detection or Phase 
Detection. A conductor used solely for instrumentation, voltage detection, or 
phase detection and connected to a single-phase or 3-phase utility-interactive 
inverter, shall be permitted to be sized at less than the ampacity of the other 
current-carrying conductors and shall be sized equal to or larger than the 
equipment grounding conductor. 

Al Frishman
EvolvedSolar
(917) 699-6641

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to