The master-slave config types and port assignments have always been confusing. 
The quick start guide lists a config where the master is port 1 and the slave 
is port 7. I believe port 7 is called the sub-master in this config. With only 
2 inverters it functions as the slave to the master in port 1. This config has 
always worked for me.

Hope this is accurate info.
On 6/25/2020 1:35:55 PM, Chris Schaefer <[email protected]> wrote:
G'Day All,

So I started up a system recently with two Radian 8048A's. The master is 
connected to port 1 and the slave connected to port 2 with the FlexNet at port 
3. There are no OB charge controllers in the system. When the hub is polling 
(led's scrolling) nothing shows up for the slave at port 2. It's like the slave 
inverter doesn't exist. So I moved the slave and flexnet down to port 3 and 4. 
No change in the polling. I swapped out comm (factory green) cables. Again no 
change. Looking at the control board of the slave there is only one green led 
on which is located at the upper right-hand side. Otherwise no led's are on. I 
have 57v at the buss bar terminals of the inverter. Of course since there is no 
polling at the hub there is no way to view port 2 to view the slave at the Mate.

Now the only thing that I didn't do was to try and use the manual on/off 
switch-jumper to start the slave. But in the past regardless of the inverter 
being on or off it would still show up on the hub. This is a new one and I'm 
looking for some direction here.

Thanks,
Christopher-
Chris Schaefer’s
[http:www.solarandwindfx.com]
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com [http://www.solarandwindfx.com] ~ E-mail: 
[email protected] [mailto:[email protected]]

Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."
_______________________________________________ List sponsored by Redwood 
Alliance List Address: [email protected] Change listserver 
email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html 
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update 
participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to