Kirk,
Not sure if this helps but
690.31(A)  “where PV source and output circuits operating at max system
voltages greater than 30v are installed in readily accessible locations,
circuit conductors shall be guarded or installed in a raceway”

It doesn’t mention 8’ but mentions “readily accessible”. We have AHJs that
interpret that as 8’ unless a 6’ fence is installed around the array. I
don’t have a reference for those measurements though...just feedback we
have gotten from inspectors

On Fri, Jul 17, 2020 at 11:38 AM Kirk Herander <[email protected]> wrote:

> All,
> Is there a reference to this so-called "8-foot rule" that someone could
> point me to in the NEC? Thanks.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> --
Adam Katzman
Autonomous Energies
PO Box 1245
Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to