I have the same problem at my place, and a couple client's systems, with
Magnum inverter/chargers and small ~2-3kw generators (not just Honda). But
the problem appliance is microwave ovens, doesn't matter which microwave
brand. They run fine straight from the generator, and fine from the
inverter with no generator running, but make a strange, loud hum, dim
internal light, and food doesn't heat if the generator is also charging the
battery bank. I'll try to figure out how to capture a waveform photo with
my scopemeter and post it.
Dan Fink
Executive Director, Buckville Energy Consulting
NABCEP PV Associate
NABCEP Certified PV System Inspector
IREC Certified Instructorâ„¢ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP Registered Continuing Education Providers
d <[email protected]>[email protected]
970-672-4342




On Sat, Aug 15, 2020 at 9:37 AM Kent Osterberg <[email protected]> wrote:

> Matt,
>
> I haven't looked at what the FXR does to the waveform of a 3000-watt
> Honda, but I have used an oscilloscope to look at the waveform of a small
> generator while an FX inverter is charging batteries -- it pretty much
> makes an ugly mess of the voltage waveform. Not surprised to hear that some
> loads don't like to operate when the FXR is charging batteries from a small
> generator. The FX charger has a poor power factor and little filtering of
> the current waveform, it is a tough load on a small generator. The
> generator responds with lots of harmonic voltages and high frequency noise.
>
> Kent Osterberg
> Blue Mountain Solar
>
>
> On 8/15/2020 8:06 AM, Matt Sherald wrote:
>
> Hello All,
>
> My curiosity was piqued by a recent customer complaint.  I'm hoping
> someone has bumped up against this issue before.
>
> The customer has a OB FXR2812 and a 3,000W Honda gen.
> Her gas clothes dryer runs just fine off the OB inverter.
> It runs properly on the Honda gen (when the inverter is bypassed)
> It will not run when the gen is on and battery charging is taking place.
>
> All the other AC loads (including the washing machine) run properly during
> battery charging with the gen.
> The OB inverter replaced an old Trace unit.  The dryer worked as it should
> with the Trace during battery charging.
>
> Any thoughts are greatly appreciated.  Thanks in advance!
>
> --
> Matt Sherald
> PIMBY Energy, LLC
> NABCEP Certified Solar PV Installer®
> 304-704-5943
>
> www.getpimby.blogspot.com
> www.getpimby.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to