Yes, seems a little heavy handed to require this so quickly out of the
gates.  This is Rocky Mountain Power specifically Eastern Utah, owned or
operated by Pacific Corp.  This may be a way to get the customer to pay for
a transformer upgrade.  They offered an alternative to this compliance
by utilizing an effective grounding transformer with associated relay
control system.  I am gathering info on these requirements because its not
clear if this is a utility side transformer or if that would be customer
sided.

They seem to be very concerned about these distributed resources
contributing to transient overvoltage events.

I will say that this area has a very high proportion of solar, its on most
homes in this community, so I'm not sure how wide-spread this requirement
is.


On Wed, Aug 26, 2020 at 7:13 PM Harry Mahon <[email protected]>
wrote:

> Mac – what utility is this?
>
>
>
> My understanding is that IEEE 1547.1-2020 contains the details of the
> testing protocol so that devices CAN be listed to 1547-2018.  It got
> published in late May 2020.
>
>
>
> Are ANY inverters listed yet?  My understanding is testing is a months
> long process and that would if the testing facilities have finalized the
> process they will use.
>
>
>
> Sounds like a way to force the transformer choice on you…
>
>
>
> Mike
>
>
>
> SMA America
> *Michael Mahon*
> Technical Trainer, Solar Academy
> 6020 West Oaks Boulevard, Suite 300
>
> Rocklin, CA 95765
>
> U.S.A.
> Mobile:   +1 916 918 9412
> * www.SMA-America.com <http://www.sma-america.com/>*
>
>
>
> Solar Academy: https://solaracademy.sma.de/en.html
>
>
>
> SMA America Solar Academy webinars:
> https://solaracademy.sma.de/en/courses.html
>
> Choose "United States"
>
> [image: A picture containing drawing, food Description automatically
> generated]
> <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2FShadeFix&data=02%7C01%7CMichael.Mahon%40sma-america.com%7Ceb737bd7586646b4d14b08d811405661%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637278315315432372&sdata=uyZ5K7ayyl6y%2Fa90qQ0%2F4r8WSV0PYLK1CYMJQxPVeCQ%3D&reserved=0>
>
>
>
> [image: Linkedin Logo] <http://www.linkedin.com/company/364675>
> <http://www.youtube.com/playlist?list=PL840A5336CAC32332> [image:
> SMAAFORUM_ICON] <http://smaadvance.com/signup/> Follow, Like, Share
>
>
>
> This email and any attachments thereto may contain SMA America, LLC
> confidential, privileged and private material for the sole use of the
> intended recipient. Any review, copying, or distribution of this email (or
> any attachments thereto) by others is strictly prohibited. If you are not
> the intended recipient, please contact the sender immediately and
> permanently delete the original and any copies of this email and any
> attachments thereto. Thank you.
>
>
>
> *From:* RE-wrenches <[email protected]> *On
> Behalf Of *Mac Lewis
> *Sent:* Wednesday, August 26, 2020 4:47 PM
> *To:* RE-wrenches <[email protected]>
> *Subject:* [RE-wrenches] Stackable Battery-Based systems complying to
> IEEE 1547-2018 standard
>
>
>
> Hi Wrenches,
>
>
>
> I am working on a design for an all-electric home whole-house backup.  The
> utility is requiring either an inverter listed to IEEE 1547-2018 or utilize
> an effective grounding transformer with associated relay control system.
> Im unclear whether the grounding transformer is on the customer side or on
> the utility side, but I'd prefer to avoid this if possible.
>
>
>
> I probably need ~20kW of continuous backup in this case.  I prefer to have
> everything stacked if possible, but I may be able to split up my critical
> load panels.
>
>
>
> Has anyone worked through this issue?  I was planning on Sol-Ark but they
> don't comply with the IEEE 1547-2018 quite yet.  I'm open to suggestions.
>
>
>
> Thanks
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to