Hello Wrenches,
Does anyone have any insights on utility transformer sizing. We are
building a micro grid and connecting two, 200 A services, which are
each currently fed by15 kVA transformers. Ohm's Law says that these
transformers would be able to supply 62.5 A at 240 V. A 200 A
service requires a 4/0 AL feed. The transformer can supply 31% of
the service rating.
The upgrade is to a 400 A service. The transformer is rated at 37.5
kVA, which would produce 156.25 A at 240 V, and will require 350
kcmil AL cable. This transformer will supply 39% of the rated 400 A.
This could only make any sense with fully imbalanced loads at nearly
max output, and we are required to balance the phases. The larger
loads are supplied by 240 V. Even in a fully imbalanced condition,
the main breakers would trip to clear any overloads if the 37.5 kVA
transformer were run to a 200 A service.
Is there really a good reason for these specifications?
Thanks,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org