That's a really interesting failure mode. I would have thought the fasteners would have pulled out but I guess it makes sense that the metal ripped.
On Mon, Oct 19, 2020 at 3:19 PM Jason Szumlanski < [email protected]> wrote: > I would say it was the metal itself. It was torn, so the clips that hold > the metal to the roof held, at least long enough for the metal to tear. It > is completely plausible that the point load was too high from too few > clamps. > > > > On Mon, Oct 19, 2020 at 8:16 AM Will White <[email protected]> wrote: > >> It's interesting that you experienced this as I've always told customers >> that the roof will come off the building with the array attached before the >> array comes off the metal roof. Sounds like the issue was with the >> attachment (or lack of) between the roof and the building. >> >> Thanks, >> Will >> >> -- >> *Will White* >> Curriculum Developer >> >> >> e: [email protected] >> w: www.solarenergy.org >> <https://mailtrack.io/trace/link/cdc1e1f93adb1352208990ede1e5191895d41435?url=http%3A%2F%2Fwww.solarenergy.org%2F&userId=1613865&signature=4501294306ef167a> >> >> p: 802-272-3092 >> >> NABCEP Certified PV Installation Professional >> # 093006-34 >> Do you envision a world powered by renewable energy? Be the change >> <https://mailtrack.io/trace/link/e6cb1800f9273a5c6a30eed1f13b034e522f98d4?url=http%3A%2F%2Fsolarenergy.org%2Fdonate&userId=1613865&signature=5258e2c2b91b9204> >> . >> >> >> >> On Sun, Oct 18, 2020 at 5:41 PM Jason Szumlanski < >> [email protected]> wrote: >> >>> I would add that S-5s are only as good as the roof. We saw a large >>> system (not ours) that ripped the metal right off the roof during Hurricane >>> Irma. It literally tore the meta. The panels, rails, and S-5s were still >>> connected, sitting on the ground with chunks of metal roofing still >>> attached to the S-5s. It was quite the mangled mess. We salvaged quite a >>> bit, but the client built a ground rack after this. >>> >>> To be fair, this was a totally exposed beachfront home. I don't know >>> what the spacing was on the clamps, either. >>> >>> >>> On Sun, Oct 18, 2020 at 12:00 PM Jerry Shafer <[email protected]> >>> wrote: >>> >>>> Wrenches >>>> I think what you said is totally true,"its only as good as the >>>> instalation" but here is where l differ, S-5's if installed correctly are >>>> no different than anything else installed on the roof. >>>> Jerry >>>> >>>> On Sun, Oct 18, 2020, 8:42 AM Dave Angelini Offgrid Solar < >>>> [email protected]> wrote: >>>> >>>>> The S5 is only as good as the installer. I have seen them come off >>>>> with a string of panels on an insurance inspection I did. >>>>> >>>>> I billed them and made another note in my journal of why the only >>>>> thing that should go on a metal roof is rainwater. >>>>> >>>>> >>>>> >>>>> *Dave Angelini Offgrid Solar >>>>> "we go where powerlines don't" >>>>> http://members.sti.net/offgridsolar/ >>>>> <https://mailtrack.io/trace/link/b0e6d73847b0d7d442ccbc699ac04d43af439126?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=605126a0d342965b> >>>>> e-mail [email protected] <[email protected]> >>>>> text 209 813 0060* >>>>> >>>>> On Sat, 17 Oct 2020 21:37:07 -0400, Hilton Dier III < >>>>> [email protected]> wrote: >>>>> >>>>> I'm with Jerry Shafer on this one. S-5 clamps with rails work well >>>>> without punching holes in the metal roof. If the roof is fastened well to >>>>> beefy steel C channel it should be fine. The S-5 clamps themselves are >>>>> stronger than the roofing. >>>>> >>>>> -- >>>>> Hilton Dier III >>>>> Missisquoi River Hydro >>>>> Renewable Energy Design >>>>> >>>>> _______________________________________________ >>>>> List sponsored by Redwood Alliance >>>>> >>>>> List Address: [email protected] >>>>> >>>>> Change listserver email address & settings: >>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>>> <https://mailtrack.io/trace/link/c8c10db58e3efe69734e322e5f0f31ec7e090028?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a6d485c377ef9948> >>>>> >>>>> There are two list archives for searching. When one doesn't work, try >>>>> the other: >>>>> https://www.mail-archive.com/[email protected]/ >>>>> <https://mailtrack.io/trace/link/80ddb795f7b98bd366d1e20301902285a48448c7?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=9134a5c6d328c742> >>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>>>> <https://mailtrack.io/trace/link/89119422c21805d90b1e65a9823d18b6429beb22?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a0672bf046a73a4a> >>>>> >>>>> List rules & etiquette: >>>>> http://www.re-wrenches.org/etiquette.htm >>>>> <https://mailtrack.io/trace/link/e7f280b4caffefae2ae5221a6e95738b0a8e1ef7?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c63636662dc4c972> >>>>> >>>>> Check out or update participant bios: >>>>> http://www.members.re-wrenches.org >>>>> <https://mailtrack.io/trace/link/f4613f21e20fcedacd00d5f1d67f1d1a035f01c5?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=546e95d914da3492> >>>>> >>>>> _______________________________________________ >>>> List sponsored by Redwood Alliance >>>> >>>> List Address: [email protected] >>>> >>>> Change listserver email address & settings: >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>> <https://mailtrack.io/trace/link/d09c4a018a3f914c79c5a573365a581c44918f85?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=9919692bb89981c0> >>>> >>>> There are two list archives for searching. When one doesn't work, try >>>> the other: >>>> https://www.mail-archive.com/[email protected]/ >>>> <https://mailtrack.io/trace/link/8719a9fa05b520a6e641de2778b6b9b563746174?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=6957ef11e3785853> >>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>>> <https://mailtrack.io/trace/link/1d1366c8bf04c7f0e1b6226f23cce0df9dd9317a?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4fe46c63e72c056e> >>>> >>>> List rules & etiquette: >>>> http://www.re-wrenches.org/etiquette.htm >>>> <https://mailtrack.io/trace/link/6d11167eee4b426db8fe5c2f82a71dc685453422?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5a0821f39a5a88ba> >>>> >>>> Check out or update participant bios: >>>> http://www.members.re-wrenches.org >>>> <https://mailtrack.io/trace/link/5186a7fd7f8b2c5b34c827b4a0d195c465566838?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=912938c0a5c0a496> >>>> >>>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> List Address: [email protected] >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> <https://mailtrack.io/trace/link/3e17d1f887ac2dfb75b9bd5df3eab7433c8c2a21?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=54c9aa37852e7c0a> >>> >>> There are two list archives for searching. When one doesn't work, try >>> the other: >>> https://www.mail-archive.com/[email protected]/ >>> <https://mailtrack.io/trace/link/e1ccde8c9d90368f5cb4cf43c64dc43dfe1eae6b?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=c36947f935e34b75> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> <https://mailtrack.io/trace/link/aa6d3bb17cf65a627bb6ea1443c48aca29f813a4?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0abe6717395cffce> >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> <https://mailtrack.io/trace/link/b2cc40b6003c2a9ecf37ad6c8ded142d973d2f41?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=591093c0f0e4bff9> >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org >>> <https://mailtrack.io/trace/link/ff6646aabf0e5259dec21558c50e1ec770277cbf?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6bf54ae82a6f4e6d> >>> >>> >> >> -- >> *Will White* >> Curriculum Developer >> >> >> e: [email protected] >> w: www.solarenergy.org >> <https://mailtrack.io/trace/link/ef9fa8ae274b7c3fa44d2a7b30bb913a58a28604?url=http%3A%2F%2Fwww.solarenergy.org%2F&userId=1613865&signature=61cf2a534b979392> >> >> p: 802-272-3092 >> >> NABCEP Certified PV Installation Professional >> # 093006-34 >> Do you envision a world powered by renewable energy? Be the change >> <https://mailtrack.io/trace/link/61716fecdb9979b27f4e4840f48da17cb24c7f86?url=http%3A%2F%2Fsolarenergy.org%2Fdonate&userId=1613865&signature=7c55952e347e348e> >> . >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <https://mailtrack.io/trace/link/3895c94afa6a7a88bc5f23e67602ea1e1b0b8782?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=08d14f3327e837e5> >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> <https://mailtrack.io/trace/link/f30751baf41fd6b80bc73b054ecbc41f7fa21870?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=022f14b73b8cc755> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> <https://mailtrack.io/trace/link/07a9c4a8a8e4afec4f3420e5b6a22296abf97347?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ecf18b45342c2cf5> >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> <https://mailtrack.io/trace/link/fd368ed3f953b1ec3569005f70831aba34e7ff42?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4d93121e20ce2b74> >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> <https://mailtrack.io/trace/link/3046e867c49ade4fc36786e601c1ad62b69809a6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=aefaab75d3a6aa98> >> >> _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > -- *Will White* Curriculum Developer e: [email protected] w: www.solarenergy.org p: 802-272-3092 NABCEP Certified PV Installation Professional # 093006-34 Do you envision a world powered by renewable energy? Be the change <http://solarenergy.org/donate>.
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org