Dave,
Looking at 2014, NEC 250.24(B) FPN and exhibits tends to imply bonding at first 
means of disconnect. This also minimizes potential ground loops.
Best regards,
Lloyd Hoffstatter
Sunstruck Consulting

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: RE-wrenches <[email protected]> on behalf of Dave 
Tedeyan <[email protected]>
Sent: Thursday, October 29, 2020 9:56:47 AM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] unfused disconnect before service disconnect

I'm looking to the hive mind here to see if others can weigh in on an issue I 
am having with an inspector. Grid tied PV system, with a line side tap in an 
automatic transfer switch. There is an outdoor utility required system 
disconnect right next to the transfer switch. But there was not enough physical 
space to get something that was service rated with overcurrent protection. So 
we installed a QO200TR, which is a tiny switch that looks like a circuit 
breaker, is rated at 60A, but does not actually have overcurrent protection. 
Then just inside the basement is the service disconnect with the neutral ground 
bond, etc. The inspector is telling me to bond the neutral and ground in the 
outdoor unfused disconnect, and remove it in the disconnect in the basement.

I am having trouble finding a code reference. Does anyone know of one showing 
that the unfused disconnect is not the service point even though it comes 
first? Or is this not something that is allowed? We are on NEC 2017 here in NY..
.
Thanks!
-Dave

Dave Tedeyan, PE
Senior Engineer | Taitem Engineering, PC
[https://www.taitem.com/signatures/logo.png]
110 South Albany Street | Ithaca, NY 14850
o. 607.277.1118 x121  f. 607.277.2119
www.taitem.com<http://www.taitem.com>

Solar • Sustainability • Energy • Design
Certified B-Corporation since 2013
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to