Once again we the installers are “guinea pigs”. Lost opportunity costs born by 
the installer believing that the components, we are selling &  installing are 
ready for prime time. Must be nice to have a “Tech” drive to Humboldt, we here 
in Maine aren’t that lucky.
> On Nov 24, 2020, at 6:42 AM, [email protected] wrote:
> 
> Thanks for this, it is really helpful.  Chris
> 
>  
> 
> 
> On 2020-11-23 11:26, Jamie Rennie wrote:
> 
>> Wrenches,
>>  
>> Enphase Encharge debacle continues. Installed the USB extension device 
>> (https://www.amazon.com/gp/product/B073B84CY1/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1
>>  
>> <https://www.amazon.com/gp/product/B073B84CY1/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1>)
>>  Enphase field engineer's recommended week before last. Once installed had 
>> good com to all the units but only 5 of the 6 batteries were communicating. 
>> Tried unsuccessfully to provision the new battery several times with tech 
>> support. Got pretty upset with the tech who was requesting I do the same 
>> sequence of events I had been trying for the last two week with no results. 
>> Asked if they had someone locally who could look at the system. Enphase 
>> field engineer (Adam Rich) called me the next day and agreed to drive up 
>> from the Bay Area to take a look at the system. Met him on site on Friday 
>> last week, went through the same trouble shooting steps and was unsuccessful 
>> in provisioning the battery even though my phone and the Envoy could "see" 
>> the battery. He tried it on his phone and it worked so the only thing we 
>> could come up with is my phone was the issue. I have a Motorola X Pure from 
>> 2016 with Android 6.0 software, Adam was using an iphone, not sure which 
>> version. Looks like I need to buy a new phone to work on these systems... 
>> Sigh
>>  
>> Later that evening I got a call from Adam and he found a separate issue with 
>> another battery. One of the microinverters on the battery was not working. 
>> Adam drove back over to the site that evening and tried to hot swap the 
>> inverter. Turns out it is a bad slot and the battery needs to be replaced. 
>> So looks like we are looking at another RMA for this system. Sharing this 
>> info with Wrenches in the hopes that it helps others evaluate these products 
>> as I have found value in the messages I have read here. I really like these 
>> new Enphase systems and stoked Enphase was kind enough to send someone out 
>> to look at our install. Seems like Enphase still has a bunch of stuff to 
>> work out on these new batteries, unfortunately we are the guinea pigs for 
>> this new technology. Hopefully our customer remains a good sport and doesn't 
>> ask us to take it all down...
>> 
>> On Tue, Nov 10, 2020 at 7:28 AM Jamie Rennie <[email protected] 
>> <mailto:[email protected]>> wrote:
>> Wrenches,
>>  
>> We just got through installing and commissioning our first Enphase system 
>> with Empower Smart switch and 2 of the Encharge 10's. Commissioning took a 
>> long time (over a week) and was really clunky with many calls to tech 
>> support. Everytime we got past one issue we ran into something else that 
>> needed to be resolved by an engineer. Most of it had to do with software and 
>> communication between envoy and other components. Found one of the batteries 
>> failed and we have replaced it. Now the batteries are not communicating with 
>> the Envoy and waiting to hear back from tech support about a solution for 
>> improving the communication between the Envoy, Empower and Encharge Units 
>> (currently IQ Combiner with Envoy is installed on East exterior wall near 
>> service and batteries are in the garage approx 60' away).  Sounds like 
>> Enphase does not have a repeater they recommend for their system yet and 
>> there are known issues with weak comm between batteries and Envoy. 
>> 
>> On Wed, Oct 7, 2020 at 10:07 AM <[email protected] 
>> <mailto:[email protected]>> wrote:
>> Thanks for that advice, Louis. Next time I will start the necessary 
>> downloads first.
>> This week with a site visit from Enphase tech support we determined the 
>> Enpower switch was stuck in an unknown state. This was resolved 
>> successfully, and now the Enpower switch and Encharge batteries are 
>> commissioned and functional. Their status and power flow can be seen on 
>> Enlighten.
>> During functional testing we determined that a major cause of the system 
>> going down when off-grid is that the well pump turn-on surge is too much for 
>> the two Encharge3 batteries.
>> This issue should be able to be solved by a motor soft starter.  Enphase 
>> recommends SureStart from Hyper Engineering. These are made for larger A/C 
>> units with access to separate fan and compressor windings so are not 
>> appropriate for this two-wire 3/4 hp well pump.
>> Does anyone have a recommendation for a suitable soft start rated at 
>> something like 8 amps load, 16 amps surge?
>>  
>> Don Barch
>> Energy Solar
>> -------- Original Message --------
>> Subject: Re: [RE-wrenches] Commissioning issues with Enphase Ensemble
>> From: Louis Woofenden <[email protected] <mailto:[email protected]>>
>> Date: Thu, October 01, 2020 3:54 pm
>> To: [email protected] <mailto:[email protected]>
>> 
>> 
>> Hi Don,
>> 
>> I have commissioned four new Ensemble systems over the past two weeks. All 
>> storage additions to existing PV systems with Enphase microinverters. 
>> Although there are parts of the process that are a bit clunky, we have not 
>> had the problems you mention. I followed the instructions in the tech brief 
>> "Ensemble Commissioning via Installer Toolkit 3.0," linked at 
>> https://enphase.com/en-us/certification-support-program-guidelines 
>> <https://enphase.com/en-us/certification-support-program-guidelines> (direct 
>> link to the PDF is 
>> https://enphase.com/sites/default/files/Tech%20Brief%20-%20Ensemble%20Commissioning%20via%20Installer%20Toolkit%203.0.pdf
>>  
>> <https://enphase.com/sites/default/files/Tech%20Brief%20-%20Ensemble%20Commissioning%20via%20Installer%20Toolkit%203.0.pdf>).
>> 
>> My experience is that each of the four Enpower microgrid interconnection 
>> devices we've installed started up in passthrough mode, so if input breakers 
>> are on in the MID, backup loads have had power before commissioning is 
>> completed, and power has remained on for those backup loads even after we 
>> turned off the PV and ESS disconnects to wait for utility PTO after doing 
>> commissioning and functional testing.
>> 
>> It did take us some time to do the Envoy software update before 
>> commissioning, and the system does require a second trip for functional 
>> testing after the Encharge battery software updates have been done (up to 12 
>> hours). I haven't stuck on site for the Encharge/Enpower software updates, 
>> but it looks like they are taking 4-6 hours for us, based on percentage done 
>> by the time I've left the site (system sizes from 10.08 kWh to 20.16 kWh). 
>> Yeah, it's a second trip. I've used the trip to meet with electrical 
>> inspectors for these first systems. 
>> 
>> One "trick" I've used on the Envoy software update is that you once you scan 
>> in the serial numbers of each Enpower & Encharge with the installer toolkit 
>> and plug in the cell modem and wireless communications kit, the installer 
>> toolkit will allow the Envoy software update to work, and you can get it 
>> taken care of early in the day, while still hanging boxes, running conduit, 
>> etc. 
>> 
>> I would agree that there are definitely parts of the new installer toolkit 
>> that aren't intuitive. I missed the "edit" button on the devices page for a 
>> bit (which is not mentioned in the tech brief), and couldn't figure out how 
>> to increase the device count, for example. I also had to try the Envoy 
>> update twice for some of these systems, as it threw an error code the first 
>> time around, so for some of the systems it took closer to 45-50 minutes to 
>> get the Envoy software update done. 
>> 
>> Hope the next one goes more smoothly for you! New products, new challenges, 
>> I guess.
>> 
>> Best,
>> 
>> Louis Woofenden
>> 
>> 
>> [email protected] <mailto:[email protected]> wrote on 9/30/20 
>> 2:59 PM:
>>> Wrenches-
>>> I'm having a lot of difficulty commissioning my first Enphase Ensemble 
>>> installation. This is on a pre-existing microinverter installation.  Have 
>>> been on the phone with tech support several times; each time they forward a 
>>> Tech Brief about commissioning that has different and slightly conflicting 
>>> instructions. It seems the order of turning on each box is critical. 
>>> Because of already-obsolete software that they ship with, the software must 
>>> be updated before activating the Envoy, Enpower, and Encharge or they will 
>>> not work.
>>> And for some reason the Envoy must have both Wifi and cell connection 
>>> before even starting commissioning, but the slower cell connection is used 
>>> for software download so it takes up to 12 hours.
>>> This commissioning must be done on-site using their latest version of 
>>> Installer Toolkit on a smart phone. Sure, there are buttons in Enlighten's 
>>> Activation page to add an Enpower and Encharge, but these do not work "yet".
>>> Enphase tech support says they are working on making this a single-day 
>>> process rather than the current multi-day commissioning. This does not even 
>>> count the actual hardware installation time.
>>>  
>>> I would advise anyone against moving any loads to a new subpanel before the 
>>> entire system is commissioned and operating.
>>> As of now I have an Enpower that mistakenly thinks it is off-grid when the 
>>> grid is present, so it has told the Envoy to shut down the PV 
>>> microinverters and batteries. These are relay controlled, therefore it is 
>>> not possible to have them connected without software control.  It has 
>>> already committed the major crime of shutting down the backed-up loads 
>>> while the grid is still present. Enphase is working on it, but seem to be 
>>> developing software on the fly. I suppose their integration process has 
>>> been hit hard by pandemic distancing, and they are all working remotely.
>>>  
>>> Has anyone else had a successful experience commissioning an Ensemble?
>>> I'd like to hear about the doos-and-don'ts.
>>>  
>>> Don Barch
>>> [email protected] <mailto:[email protected]>
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> 
>> -- 
>> -- 
>> Louis Woofenden
>> Engineering Director
>> Net Zero Solar, LLC
>> 101. W. 5th St., Tucson, AZ 85705
>> Arizona ROC #248710, 259756, 259521 
>> 
>> Phone: 520.207.4053 <tel:520.207.4053> Ex. 3
>> Cell: 520.237.5040 <tel:520.237.5040>
>> Fax: 520.203.7230 <tel:520.203.7230>
>> 
>> NABCEP Certified PV Installation Professional™
>> 
>>  
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>>  
>> -- 
>> Respectfully,
>>  
>> Jamie Rennie
>> Greenwired
>> P: 707-923-2001 <tel:707-923-2001>C: 707-273-7387
>> 1150 #1 Evergreen Rd
>> Redway, CA 95560
>> www.greenwired.com <http://www.greenwired.com/>
>> 
>>  
>> -- 
>> Respectfully,
>>  
>> Jamie Rennie
>> Greenwired
>> P: 707-923-2001 <tel:707-923-2001>C: 707-273-7387
>> 1150 #1 Evergreen Rd
>> Redway, CA 95560
>> www.greenwired.com <http://www.greenwired.com/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

> [email protected] 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to