Wrenches:


I found some time to review the .evt and .log files from the primary Sunny
Island inverter.



Prior to 12/8/20 the system was running normally with a generator run
averaging 6 hours about every other day.



On 12/8 at 06:00 the system tried to start the generator.  There was no
indication the generator delivered voltage to the system.  The system tried
to start the generator 168 times between 12/18 at 06:00 and 12/13 at
15:00.  168 times the system closed relay 1 and then opened it about 2
minutes later.  Maybe the generator ran, maybe it didn’t, but no voltage
was delivered.  On 12/15 the client started the generator and it produced
voltage into the inverter system.  On 12/18 I started the generator and it
produced voltage.



Why this generator start cycle kept recurring is a mystery to me.  There
may be a setting within the bowels of the menu system that I have
overlooked that limits the start attempts and I will be investigating
that.  To me, navigating the Sunny Island menu system is like trying to
remember the DOS command-line interface.  I need something much more
ergonomic.



Thanks for all of your priceless knowledge.  I feel like we are a little
nerd family.



William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to