Hello Andrew,

I find your opinion on needing Rapid Shutdown. Critters chewing on wires is the 
reason why they implemented article 690.11 of the NEC, arc fault detection. 

What does module level shut down do? Well mostly nothing, especially in energy 
storage systems. In standard grid-tie systems IF the inverter detects the arc, 
the inverter will shut down. Most Rapid shutdown solutions are PLC solutions, 
so the inverter trips off, and then the voltage gets reduced to less than 80v 
within the array boundary (rapid shutdown activated). 80v is still high enough 
for a sustainable arc to occur that can melt MC4s. 

If the same rapid shutdown topology is for an energy storage system, rapid 
shutdown won't occur (an inverter error keeps RSD active, due to Energy 
storage). So in reality the rapid shutdown devices doesn't do a thing. 


Sustainable regards,
Chris Connell




-----Original Message-----
From: RE-wrenches [mailto:[email protected]] On Behalf 
Of [email protected]
Sent: Friday, January 29, 2021 4:53 PM
To: [email protected]
Subject: [GREY] RE-wrenches Digest, Vol 14, Issue 28

Send RE-wrenches mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
        http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
or, via email, send a message with subject or body 'help' to
        [email protected]

You can reach the person managing the list at
        [email protected]

When replying, please edit your Subject line so it is more specific than "Re: 
Contents of RE-wrenches digest..."


When responding to posts within the Digest, be sure to restore the Subject: 
line to the original, and please edit out any extraneous lines from the quoted 
message.
 

Today's Topics:

   1. MLSD module level shutdown ([email protected])
   2. Re: MLSD module level shutdown (Solar Energy Solutions)
   3. Re: MLSD module level shutdown (Kristopher Schmid)
   4. Re: MLSD module level shutdown (frenergy)
   5. Re: MLSD module level shutdown (Dave Angelini Offgrid Solar)
   6. Re: MLSD module level shutdown (Ray)
   7. Re: MLSD module level shutdown (Dave Angelini Offgrid Solar)


----------------------------------------------------------------------

Message: 1
Date: Fri, 29 Jan 2021 14:09:48 -0500
From: [email protected]
To: [email protected]
Cc: Melissa Ann MacCarthy <[email protected]>
Subject: [RE-wrenches] MLSD module level shutdown
Message-ID:
        <[email protected]>
Content-Type: text/plain; charset=utf-8

So far the module level shutdown requirements have been a real blow to our 
industry. The reliability and cost from a maintenance and installation 
standpoint has been very hit or miss so far. It feels like this requirement was 
rolled out far too quickly without enough forethought to its impact on the 
industry. We are constantly going out and fixing problems with mlsd installed 
by other contractors. Thankfully the problems have nothing to do with the 
quality of the installations. The problems are almost all due to premature 
failure of the products or some inherent defect in them. This is a serious 
issue costing the industry time and resources and making our installers less 
safe. It just doesn?t really accomplish the intended goal of the requirement. 
I?m curious how other wrenches are dealing with this issue. I recently became 
aware of fixMLSD.com which appears to be focused on bringing a more sensible 
approach to this requirement. 

Your thoughts are appreciated,
Sky Sims
Https://EcologicalSystems.biz
?Just An Old Wrench?

------------------------------

Message: 2
Date: Fri, 29 Jan 2021 19:56:08 +0000 (UTC)
From: Solar Energy Solutions <[email protected]>
To: "[email protected]"
        <[email protected]>
Cc: Melissa Ann MacCarthy <[email protected]>
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"

Dear All,
I have been an outspoken critic of module level shutdown for all the reasons 
folks do.? However, I have come around.? We have witnessed too many systems 
where rooftop wiring has been chewed up by critters... mostly squirrels.? We 
have seen everything from residential fires to holes in metal roofs caused by a 
DC arc.?? I never thought I would see the day when I would not only be thinking 
MLSD is a good idea but advocating for it.

Smiles,
?Andrew KoyaanisqatsiPresidentSolar Energy Solutions, Inc.
The BRIGHT CHOICE
Since 1987, helping you and your Portland neighbors move towards an 
environmentally sustainable future.503-238-4502 www.SolarEnergyOregon.com  

    On Friday, January 29, 2021, 11:25:28 AM PST, [email protected] 
<[email protected]> wrote:  
 
 So far the module level shutdown requirements have been a real blow to our 
industry. The reliability and cost from a maintenance and installation 
standpoint has been very hit or miss so far. It feels like this requirement was 
rolled out far too quickly without enough forethought to its impact on the 
industry. We are constantly going out and fixing problems with mlsd installed 
by other contractors. Thankfully the problems have nothing to do with the 
quality of the installations. The problems are almost all due to premature 
failure of the products or some inherent defect in them. This is a serious 
issue costing the industry time and resources and making our installers less 
safe. It just doesn?t really accomplish the intended goal of the requirement. 
I?m curious how other wrenches are dealing with this issue. I recently became 
aware of fixMLSD.com which appears to be focused on bringing a more sensible 
approach to this requirement. 

Your thoughts are appreciated,
Sky Sims
Https://EcologicalSystems.biz
?Just An Old Wrench?
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20210129/c80252ee/attachment-0001.html>

------------------------------

Message: 3
Date: Fri, 29 Jan 2021 14:17:06 -0600
From: Kristopher Schmid <[email protected]>
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID:
        <cajb-is-9cisjjyalsuiorrbuhmdm4zwnpvs8afwqvs-ydgo...@mail.gmail.com>
Content-Type: text/plain; charset="utf-8"

Sky,

I, for one, totally agree.  While I agree with the need to keep firefighters 
safe, it seems to me that rules regarding solar conduit would serve the same 
purpose; required labeling of rooftop conduit beyond the array boundary, 
required distance below roof deck for attic conduit, etc.
I am sure that there is a fair amount of lobbying by SolarEdge and Enphase to 
keep the rapid shutdown rules unchanged and retain their market share.
While MLPE have their place in the industry, they should not be the only viable 
choice for a roof mounted array.


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional Licensed Wisconsin Master 
Electrician BSEE


On Fri, Jan 29, 2021 at 1:25 PM <[email protected]> wrote:

> So far the module level shutdown requirements have been a real blow to 
> our industry. The reliability and cost from a maintenance and 
> installation standpoint has been very hit or miss so far. It feels 
> like this requirement was rolled out far too quickly without enough 
> forethought to its impact on the industry. We are constantly going out 
> and fixing problems with mlsd installed by other contractors. 
> Thankfully the problems have nothing to do with the quality of the 
> installations. The problems are almost all due to premature failure of 
> the products or some inherent defect in them. This is a serious issue 
> costing the industry time and resources and making our installers less 
> safe. It just doesn?t really accomplish the intended goal of the requirement.
> I?m curious how other wrenches are dealing with this issue. I recently 
> became aware of fixMLSD.com which appears to be focused on bringing a 
> more sensible approach to this requirement.
>
> Your thoughts are appreciated,
> Sky Sims
> Https://EcologicalSystems.biz
> ?Just An Old Wrench?
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try 
> the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20210129/e2d8f2cd/attachment-0001.html>

------------------------------

Message: 4
Date: Fri, 29 Jan 2021 12:58:08 -0800
From: frenergy <[email protected]>
To: [email protected]
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"; Format="flowed"

Andrew,

 ??? ??? ??? If these are the only two examples of justification of MLSD and 
not knowing the details of the examples you've cited, I suggest there is a more 
effective, equal in labor to apply, less expensive, durable solution.? For the 
squirrel problem, an alternate solution is one of the available edge of array 
screen products.? Not only does it stop the squirrels but it works for mice, 
leaves, pine needles, etc.

 ??? ??? ??? Can you enlighten us about the cause of the resi fires that were 
caused from the lack of MLSD's?? Poor wire management? And was the hole in the 
metal roof caused by the squirrel having lunch on the wiring?

 ??? ??? ??? I feel it worth diving into this deeper for a variety of reasons.

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net

On 1/29/2021 11:56 AM, Solar Energy Solutions wrote:
> Dear All,
>
> I have been an outspoken critic of module level shutdown for all the 
> reasons folks do.? However, I have come around.? We have witnessed too 
> many systems where rooftop wiring has been chewed up by critters...
> mostly squirrels.? We have seen everything from residential fires to 
> holes in metal roofs caused by a DC arc.?? I never thought I would see 
> the day when I would not only be thinking MLSD is a good idea but 
> advocating for it.
>
> Smiles,
> **Andrew Koyaanisqatsi**
> *President*
> **Solar Energy Solutions, Inc.
> /The BRIGHT CHOICE/
> **
> *Since 1987,**helping you and your Portland neighbors move**towards an 
> environmentally sustainable future.*
> **503-238-4502
> www.SolarEnergyOregon.com <http://www.solarenergyoregon.com/> **
>
>
> On Friday, January 29, 2021, 11:25:28 AM PST, 
> [email protected] <[email protected]> wrote:
>
>
> So far the module level shutdown requirements have been a real blow to 
> our industry. The reliability and cost from a maintenance and 
> installation standpoint has been very hit or miss so far. It feels 
> like this requirement was rolled out far too quickly without enough 
> forethought to its impact on the industry. We are constantly going out 
> and fixing problems with mlsd installed by other contractors.
> Thankfully the problems have nothing to do with the quality of the 
> installations. The problems are almost all due to premature failure of 
> the products or some inherent defect in them. This is a serious issue 
> costing the industry time and resources and making our installers less 
> safe. It just doesn?t really accomplish the intended goal of the 
> requirement.
> I?m curious how other wrenches are dealing with this issue. I recently 
> became aware of fixMLSD.com which appears to be focused on bringing a 
> more sensible approach to this requirement.
>
> Your thoughts are appreciated,
> Sky Sims
> Https://EcologicalSystems.biz
> ?Just An Old Wrench?
> _______________________________________________
>
-- 



--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20210129/dfccba2d/attachment-0001.html>

------------------------------

Message: 5
Date: Fri, 29 Jan 2021 13:32:30 -0800
From: Dave Angelini Offgrid Solar <[email protected]>
To: "RE-wrenches" <[email protected]>
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID: <[email protected]>
Content-Type: text/plain; charset=UTF-8

Hi Sly,

 The small part of the industry ( Offgrid ) mostly uses ground mounting and is 
not using MLSD. On some new offgrid homes I use rapid shutdown at MPPT level to 
get the permit if the AHJ can't be reasoned with. The Schneider rapid shutdown 
has a nice 600 vdc disconnect in it,  that is useful later if the homeowner 
decides to abandon the extra electronics that can affect reliability.

We also protect the area under and near the modules to guard against a rare 
defect from causing a wildfire.

I would like to hear what Outback is doing for this also from you guys please?  
FRIDAY !!!


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail [email protected]
text 209 813 0060

On Fri, 29 Jan 2021 14:09:48 -0500, [email protected] wrote:
> So far the module level shutdown requirements have been a real blow to
our
> industry. The reliability and cost from a maintenance and installation 
> standpoint has been very hit or miss so far. It feels like this
requirement
> was rolled out far too quickly without enough forethought to its 
> impact
on
> the industry. We are constantly going out and fixing problems with 
> mlsd installed by other contractors. Thankfully the problems have 
> nothing to
do
> with the quality of the installations. The problems are almost all due
to
> premature failure of the products or some inherent defect in them. 
> This
is
> a serious issue costing the industry time and resources and making our 
> installers less safe. It just doesn?t really accomplish the intended
goal
> of the requirement. 
> I?m curious how other wrenches are dealing with this issue. I recently 
> became aware of fixMLSD.com which appears to be focused on bringing a
more
> sensible approach to this requirement. 
> 
> Your thoughts are appreciated,
> Sky Sims
> Https://EcologicalSystems.biz
> ?Just An Old Wrench?
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try
the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org


------------------------------

Message: 6
Date: Fri, 29 Jan 2021 17:26:49 -0500
From: Ray <[email protected]>
To: [email protected]
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"; Format="flowed"

Yes, I would like more info too.? I'm all about safety, but it needs to be 
based on reality not theory.? For instance, would string level shut down have 
stopped the arcs you mentioned?? Also, I second the screening.? Even if MLSD 
stops the fire, the rodents have still won the day by taking out part of the 
array.? How about an exemption from MLSD for systems below a certain voltage, 
and having animal guard in place, and those would still have string level shut 
down.

Ray Walters
Remote Solar
303 505-8760

On 1/29/21 3:58 PM, frenergy wrote:
>
> Andrew,
>
> ??? ??? ??? If these are the only two examples of justification of 
> MLSD and not knowing the details of the examples you've cited, I 
> suggest there is a more effective, equal in labor to apply, less 
> expensive, durable solution.? For the squirrel problem, an alternate 
> solution is one of the available edge of array screen products.? Not 
> only does it stop the squirrels but it works for mice, leaves, pine 
> needles, etc.
>
> ??? ??? ??? Can you enlighten us about the cause of the resi fires 
> that were caused from the lack of MLSD's?? Poor wire management? And 
> was the hole in the metal roof caused by the squirrel having lunch on 
> the wiring?
>
> ??? ??? ??? I feel it worth diving into this deeper for a variety of 
> reasons.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
> On 1/29/2021 11:56 AM, Solar Energy Solutions wrote:
>> Dear All,
>>
>> I have been an outspoken critic of module level shutdown for all the 
>> reasons folks do.? However, I have come around.? We have witnessed 
>> too many systems where rooftop wiring has been chewed up by 
>> critters... mostly squirrels.? We have seen everything from 
>> residential fires to holes in metal roofs caused by a DC arc.?? I 
>> never thought I would see the day when I would not only be thinking 
>> MLSD is a good idea but advocating for it.
>>
>> Smiles,
>> **Andrew Koyaanisqatsi**
>> *President*
>> **Solar Energy Solutions, Inc.
>> /The BRIGHT CHOICE/
>> **
>> *Since 1987,**helping you and your Portland neighbors move**towards 
>> an environmentally sustainable future.*
>> **503-238-4502
>> www.SolarEnergyOregon.com <http://www.solarenergyoregon.com/> **
>>
>>
>> On Friday, January 29, 2021, 11:25:28 AM PST, 
>> [email protected] <[email protected]> wrote:
>>
>>
>> So far the module level shutdown requirements have been a real blow 
>> to our industry. The reliability and cost from a maintenance and 
>> installation standpoint has been very hit or miss so far. It feels 
>> like this requirement was rolled out far too quickly without enough 
>> forethought to its impact on the industry. We are constantly going 
>> out and fixing problems with mlsd installed by other contractors.
>> Thankfully the problems have nothing to do with the quality of the 
>> installations. The problems are almost all due to premature failure 
>> of the products or some inherent defect in them. This is a serious 
>> issue costing the industry time and resources and making our 
>> installers less safe. It just doesn?t really accomplish the intended 
>> goal of the requirement.
>> I?m curious how other wrenches are dealing with this issue. I 
>> recently became aware of fixMLSD.com which appears to be focused on 
>> bringing a more sensible approach to this requirement.
>>
>> Your thoughts are appreciated,
>> Sky Sims
>> Https://EcologicalSystems.biz
>> ?Just An Old Wrench?
>> _______________________________________________
>>
> --
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>  
>       Virus-free. www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_
> campaign=sig-email&utm_content=emailclient&utm_term=link>
>
>
> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20210129/e8f416c9/attachment-0001.html>

------------------------------

Message: 7
Date: Fri, 29 Jan 2021 14:29:12 -0800
From: Dave Angelini Offgrid Solar <[email protected]>
To: "RE-wrenches" <[email protected]>
Subject: Re: [RE-wrenches] MLSD module level shutdown
Message-ID: <[email protected]>
Content-Type: text/plain; charset=UTF-8

Hi Ben,

Dave had to go on a service call up into the high county. No cell ! I expect 
him back before dark. Probably will get back in the AM

Thanks, Ingrid

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail [email protected]
text 209 813 0060

On Fri, 29 Jan 2021 13:32:30 -0800, Dave Angelini Offgrid Solar 
<[email protected]> wrote:
> Hi Sly,
> 
>  The small part of the industry ( Offgrid ) mostly uses ground 
> mounting and is not using MLSD. On some new offgrid homes I use rapid 
> shutdown at MPPT level to get the permit if the AHJ can't be reasoned 
> with. The Schneider rapid shutdown has a nice 600 vdc disconnect in 
> it,  that is useful later if the homeowner decides to abandon the 
> extra electronics
that
> can affect reliability.
> 
> We also protect the area under and near the modules to guard against a 
> rare defect from causing a wildfire.
> 
> I would like to hear what Outback is doing for this also from you guys 
> please?  FRIDAY !!!
> 
> 
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail [email protected]
> text 209 813 0060
> 
> On Fri, 29 Jan 2021 14:09:48 -0500, [email protected] wrote:
>> So far the module level shutdown requirements have been a real blow 
>> to
> our
>> industry. The reliability and cost from a maintenance and 
>> installation standpoint has been very hit or miss so far. It feels 
>> like this
> requirement
>> was rolled out far too quickly without enough forethought to its 
>> impact
> on
>> the industry. We are constantly going out and fixing problems with 
>> mlsd installed by other contractors. Thankfully the problems have 
>> nothing to
> do
>> with the quality of the installations. The problems are almost all 
>> due
> to
>> premature failure of the products or some inherent defect in them. 
>> This
> is
>> a serious issue costing the industry time and resources and making 
>> our installers less safe. It just doesn?t really accomplish the 
>> intended
> goal
>> of the requirement. 
>> I?m curious how other wrenches are dealing with this issue. I 
>> recently became aware of fixMLSD.com which appears to be focused on 
>> bringing a
> more
>> sensible approach to this requirement. 
>> 
>> Your thoughts are appreciated,
>> Sky Sims
>> Https://EcologicalSystems.biz
>> ?Just An Old Wrench?
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try
> the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try
the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org


------------------------------

Subject: Digest Footer

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



------------------------------

End of RE-wrenches Digest, Vol 14, Issue 28
*******************************************
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to