Wrenches,
You can have 4800W on L1 and 0W on L2. It has huge 240V peak power. But you are
correct that some 120V inductive loads >3/4hp can be an issue. We recommend
rewiring those massive motors to 240V (most are convertible on the motor). The
1400W limit is with DC Loads. A heat gun on high is an AC load but on low, it
only uses 1/2 of the sinewave (DC load). Our limit for DC loads (hair dryer,
leaf blower, drill, blender, curling iron, heat gun only on low setting) is
1400W.
Thank you and have a blessed day,
Dustin Douglas
Engineering Support Lead
(972)575-8875 ext. 108
http://www.Sol-Ark.com
---- On Tue, 09 Feb 2021 23:23:22 -0600 Nick A Lucchese <[email protected]>
wrote ----
I agree with many of you on waiting awhile longer until these issues are sorted
out. While I definitely think there is plenty of room beyond our usual
favorites for another robust battery based inverter to offer I don’t intend to
embark on another frustrating adventure at mostly my expense. At this point I’m
more excited for the Midnite inverters more than anything and know once they’re
released I won’t feel like I made a mistake. Meanwhile I’ll definitely be
sending wishes of success to Sol-Ark. I’ve heard a lot of good things and will
remain optimistic and hopeful it’s shortcomings will be resolved soon without
needing to stack multiple units or a transformer.
Nick A Lucchese
On Feb 9, 2021, at 12:17 PM, Dave Angelini Offgrid Solar
<mailto:[email protected]> wrote:
Yes that has happened with 2 of mine Jerry. I like the Transformer Devils that
I know. Might check these out in 2 or 3 years. The whole all in one does not
really appeal to me either but I will keep an open mind, in 2 or 3 years!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail mailto:[email protected]
text 209 813 0060
On Tue, 9 Feb 2021 10:19:44 -0800, Jerry Shafer
<mailto:[email protected]> wrote:
It is also interesting how sol ark sells over the counter to end users and also
through distributors but at nearly the same price so it makes it difficult for
our distributors to carry the sol ark products. Jerry
On Tue, Feb 9, 2021, 7:42 AM Jay <mailto:[email protected]> wrote:
It is odd that the 12kw 20kw surge sol ark can't run a 15 amp 120v air
compressor
I saw a you tube video from what appears to be a pretty well versed installer
who mentioned that sol ark knows this is an issue and specifically mentioned
that his small air compressor will shut his 12kw inverter down. He didn't
mention if there is a fix coming.
I guess I'll wait to buy one until they have that issue sorted out.
Jay
Peltz power.
_______________________________________________
List sponsored by Redwood Alliance
List Address: mailto:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org/
_______________________________________________
List sponsored by Redwood Alliance
List Address: mailto:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org