The inverters have a pretty tight frequency range, I have adjusted gennys
to run out of that tight range, they just keep waiting for the frequency to
come back. I can take a little tinkering on some models but even 57 hz is
enough if your Hawaii  with the HECo rule or California. You can go over
too but if there is a lug it may still connect the inverter.
Jerry

On Thu, Feb 25, 2021, 5:40 AM Nik Ponzio, Building Energy <
[email protected]> wrote:

> We are installing 25kW of PV on a service with an existing backup
> generator (Eaton 30KW) and auto transfer switch. Because of the remote
> location of the generator and transfer switch, we can not easily connect on
> the grid-side of the transfer switch as we usually do (without cutting a
> very long trench.) So we're looking for a way to lock out the solar during
> generator use. And then, ideally, reconnect the solar automatically when
> the grid is restored.
>
> Is there an off-the-shelf product available at this point to accomplish
> this?
>
> I see a thread on here
> <https://mailtrack.io/trace/link/7643522e54e5bd30057d2e139c7b93d1c488b655?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmsg23906.html&userId=6273276&signature=c4db635fbd2d1225>
> from a couple years ago that recommended the Generac SMM for this type of
> scenario. Any current thoughts on this approach?
>
> Any suggestions would be appreciated.
>
>
> --
> Nik Ponzio
> Building Energy
> 1570 South Brownell Road
> Williston, VT 05495
> direct: 802-318-7003
> [email protected]
> http://www.BuildingEnergyVT.com
> <https://mailtrack.io/trace/link/058e994a3bba9674653a69dd2a6976e0914d2761?url=http%3A%2F%2Fwww.BuildingEnergyVT.com&userId=6273276&signature=8b5247886585b42b>
>
>
>
> "Building Solutions for a Sustainable Future"
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to