Thanks Corey, 

I probably will use the Skybox without the battery for
the client future. He will have to change out a well pump to a softstart
pump later if he wants batteries. 

BTW Schneider XWP and CSW can run
without the transformers in a zero export mode. They run an amp on the
primary to always keep from selling. XWP can also have the power meter if
one wants to really drop the very small loss. But, you do have a battery,
which is why I will probably use the Skybox. He also is an old friend. 

I
may have a consult for you if my client makes his decision on Eleuthera
Bahamas or Jamaica. He wants palm trees....  

Dave Angelini Offgrid
Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail [email protected] [2]
text 209 813 0060

On Sun, 11 Apr 2021
12:20:39 -0500, Corey Shalanski  wrote:   Hello Dave,   As far as I know,
setting up an inverter for zero export will *always* require installation
of current transformers (CTs), and those CTs must be connected to some sort
of power meter, which in turn must be connected to some sort of control
device. Whether the power meter and/or control device are built-in or
external varies by manufacturer. See attached diagrams for several examples
by popular manufacturers:  

        * Sol-Ark: both power meter and control
device appear* to be built-in 

        * * I have never actually worked with
Sol-Ark equipment, so someone please correct if this is not the case.

        *
SolarEdge: control device is built-in, power meter is external
        * SMA:
both power meter and control device are external

  You'll note the
presence of CTs in each diagram. Both SMA [3] and SolarEdge [4] offer 6 kW
inverters; Sol-Ark [5] appears to only offer only 8 kW and 12 kW options.  
-- Corey Shalanski Jah Light Solar Portland, Jamaica   
  On Sat, Apr 10,
2021 at 8:41 AM  wrote:  

Hi Wrenches, 

I do not see much grid-tie and
never with a battery less inverter. I have a client who wants me to explore
zero export for them. I have looked at http://www.elgrispower.com/ [7] 

Is
there such a thing in a medium size 6 KW Grid inverter built-in that can
zero export? Or, Do I have to externally wire power meters ect? 


Thank-you !  

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [8]
e-mail [email protected]
[9]
text 209 813 0060
     

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
[3]
https://files.sma.de/downloads/SBxx-US-DS-en-38.pdf?_ga=2.179034083.671752729.1618086517-1642740404.1587256948
[4]
https://www.solaredge.com/sites/default/files/se-hd-wave-single-phase-inverter-with-setapp-datasheet-na.pdf
[5]
https://www.sol-ark.com/support/
[6] mailto:[email protected]
[7]
http://www.elgrispower.com/
[8] http://members.sti.net/offgridsolar/
[9]
mailto:[email protected]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to