Lou,
I spoke this morning with Kedar, who purchased Bogart Engineering several years ago, about an out-of-warranty repair on a TM-2030 (Stupid human trick - after installing maybe 100 TriMetrics over 30 years I wired a new one backwards). Remembering your post I asked him about settings for lithium batteries in general. I have done this successfully with several Blue Ion LFP battery replacement installations.
His recommendations:
- set voltage to the BMS voltage regulation setpoint (55.2 for Blue Ion)
- set amps either Off or to a high (5-10%) to disable this parameter
- Set CEF to 98-99%
- set battery AH capacity to actual rated capacity @100% DoD

I checked records for a couple of my own 2018 installations (Both of these had existing TM-2020s rather than TM-2030s, which shouldn't make any difference in their settings and operation.):
- I set voltage a bit lower - 54.0 and 54.5
- I set amps off in one case and 8A in the other
- I set a large (24 kWhr) CEF to 98% and a smaller (8 kWhr) set to 95%
And both have continued to supply accurate and usable info to the client.

By the way, I was initially disappointed to learn that Ralph Hiesey had sold his business and retired. I have recently, however, received excellent customer support from Kedar, the owner of Bogart Engineering, and wanted to pass that good review along.
Allan

On 6/4/2021 12:16 AM, Lou Russo wrote:
Aloha All,
Does anyone have experience with the TM-2030's SOC accuracy when used with LFP batteries that they are willing to share? I would think the TM-2030 would be accurate but I just want some confirmation.
Thanks.
Lou Russo
--

*Allan Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to