Hi Drake,
So it's simply a momentary bypass circuit from the Load side to the Line
side of your Main Inverter Breaker. So from battery side of inverter to
momentary on-off switch to resistor to inverter side of breaker.
I used a 25 Ohm 50 watt resistor.this one
<https://www.amazon.com/YiePhiot-Resistor-Aluminum-Wirewound-Doorbell/dp/B07MW4VHDB/ref=sr_1_13?dchild=1&keywords=YiePhiot&qid=1623685581&sr=8-13>
and this nice metal screw-terminal momentary on-off switch this one
<https://www.amazon.com/Momentary-Waterproof-Stainless-Terminal-warranty/dp/B079HR5Q4R/ref=pd_sbs_1/142-3113942-9020237?pd_rd_w=dHOiq&pf_rd_p=a5925d26-9630-40f3-a011-d858608ac88b&pf_rd_r=WSD3157P3TEAB0M4Z6PR&pd_rd_r=ab809190-b332-4f06-952b-369bf1c6a51c&pd_rd_wg=qD1Vl&pd_rd_i=B079HR5Q4R&psc=1>
With a Magnum MS4024 PAE on a 10 KWH LiFePO4 pack - when I push the
switch initially about 2 amps flows - I've found I need to hold it for
about 8 seconds for the current to drop off to about .4 amps - then when
I flip the 175 AMP main DC inverter breaker - there is little additional
current that flows into the inverter caps - no sparks and my BMS doesn't
shut down due to overcurrent fault.
Hope that helps!
Best,
Jeff
[email protected]
<mailto:[email protected]>
June 11, 2021 at 12:27 PM
Hello Jeff,
That sounds really useful. How do you wire this? Where do you get the
momentary switch?
Thanks,
Drake
---
On 2021-06-09 12:13, Jeff Clearwater wrote:
Hey Dave and Wrenches,
This is why now I always install a pre-charge circuit for Magnum's
and other inverters - especially on a Lithium pack with a BMS. A
momentary on-off switch and 50 watt 20 ohm resistor - $20 worth of
parts = a lifetime of less stress on main breaker - inverter caps
and battery BMS. I recommend it for any inverter over 2 KW. Many
LiFePO4 BMS's will shut down when sensing that much inrush so it's a
must on many systems.
Best,
Jeff Clearwater
Village Power Design
[email protected] <mailto:[email protected]>
June 8, 2021 at 6:01 AM
Is a Magnum MM1524AE inverter/charger repairable and if so by whom?
It failed after being reconnected to a battery bank, the typical
small spark at the battery terminal when being reconnected was
accompanied by a popping sound in the Magnum. Killed the Magnum.
Dave Palumbo
Hyde Park, VT
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Jeff Clearwater <mailto:[email protected]>
June 9, 2021 at 9:13 AM
Hey Dave and Wrenches,
This is why now I always install a pre-charge circuit for Magnum's and
other inverters - especially on a Lithium pack with a BMS. A
momentary on-off switch and 50 watt 20 ohm resistor - $20 worth of
parts = a lifetime of less stress on main breaker - inverter caps and
battery BMS. I recommend it for any inverter over 2 KW. Many LiFePO4
BMS's will shut down when sensing that much inrush so it's a must on
many systems.
Best,
Jeff Clearwater
Village Power Design
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Jeff Clearwater <mailto:[email protected]>
June 9, 2021 at 9:12 AM
Hey Dave and Wrenches,
This is why now I always install a pre-charge circuit for Magnum's and
other inverters - especially on a Lithium pack with a BMS. A
momentary on-off switch and 50 watt 20 ohm resistor - $20 worth of
parts = a lifetime of less stress on main breaker - inverter caps and
battery BMS. I recommend it for any inverter over 2 KW. Many LiFePO4
BMS's will shut down when sensing that much inrush so it's a must on
many systems.
Best,
Jeff Clearwater
Village Power Design
[email protected] <mailto:[email protected]>
June 8, 2021 at 6:01 AM
Is a Magnum MM1524AE inverter/charger repairable and if so by whom?
It failed after being reconnected to a battery bank, the typical small
spark at the battery terminal when being reconnected was accompanied
by a popping sound in the Magnum. Killed the Magnum.
Dave Palumbo
Hyde Park, VT
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org