William,

The LRA of an A/C system is the peak current demand. The inverter must be sized 
for that and all other potential loads if using a single inverter. For that 
reason, we have almost always used a dedicated inverter for an A/C systems and 
leave the primary inverter for all other loads. That way the A/C will start no 
matter what other loads are on the primary inverter. 

Install a hard start capacitor unit (sometimes now called soft start) if it is 
not factory equipped with one. Using Li-ion batteries is also recommended due 
to voltage sag using LA. Otherwise, you may want to size a LA bank larger for 
the additional current demand while starting.

We have been doing separate inverters for 120V RV A/C’s and 240V mini splits 
this way for years and it has been trouble free. 

Larry Crutcher
Starlight Solar Power Systems





On Jun 23, 2021, at 9:30 AM, William Miller <[email protected]> wrote:

Friends:
 
In the old days when a client suggested they might want to run air conditioning 
equipment on an off-grid system we would just laugh.  Now I find I get that 
request more frequently and clients are willing to pay to acquire enough system 
capacity to run AC equipment.
 
This means I need to size off-grid installations appropriately for the loads.  
I have a job pending with a 5 ton AC unit.  I cannot find real-life energy 
specs.
 
I do have a new, fairly efficient 3 ton unit at my grid-connected home and I do 
have energy monitoring.  On a real hot day recently we used a little less than 
11kWh in this unit.  The max power draw was about 2.5 kW.
 
Here are my questions:  
 
1.   Can I linearly extrapolate my usage to a 5 ton unit?
2.   Do any of you have real-life, measured energy data on modern AC condenser 
units that you would be willing to share?
 
Thanks in advance!
 
William Miller
 
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
 
 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>

List Address: [email protected] 
<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/ 
<https://www.mail-archive.com/[email protected]/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm 
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to