Hi William

No that’s definitely not it. 

Production of a 3.5 kWh array is at max 1 kw, with about .8kw going to the grid

Jay 

> On Jul 18, 2021, at 5:44 PM, William Miller <[email protected]> wrote:
> 
> Damaged batteries consuming power?
> 
> William Miller
> www.millersolar.com
> 
>> On Jul 18, 2021, at 12:26 PM, jay <[email protected]> wrote:
>> 
>> HI All,
>> 
>> I”m trying to diagnose the following system I didn’t install.
>> 
>> 4 year old system grid tie battery back up.
>> 
>> Radian 4048
>> flexmax 80
>> 3500 watts PV
>> fndc
>> it is on opticsRE
>> 
>> The symptoms are that its not selling much at all.  Mostly when it is about 
>> 1kw max PV production and .8kw selling.  I have disconnected the FNDC and 
>> after that it did seem to work better.  
>> 
>> Usually it will sell a bit, then buy a bit then sell and so on.  Grid 
>> voltage is very constant at around 246vac. 
>> 
>> I’ve been through the settings a few times with tech support, made 
>> adjustments and for a while it was selling pretty normally, but again today 
>> 0 production, CC is at float.  
>> 
>> I have not been to the site, I was just trying to do this all by optics.  
>> But I’m going to have to go.   I think there are 3 possible issues.  
>> 
>> 1. the customer has always thought the production is low.  And from what 
>> I’ve seen that is true.  This is in a very sunny place, no shade so with 
>> 3.5kw, 1kw is very low which I think they may have  a few strings of the 
>> array are not connected. However why that bothers me is that the VOC/VMP 
>> voltages are too close in looking at the CC.  Which leads me to think its 
>> been told to back off to the 1.0kw, by some setting, see #2. And its always 
>> around .8 selling and around 1kw output from the array. 
>> 
>> 2.  There is a programing issue.  
>> 
>> 3. There is a hardware issue.
>> 
>> 
>> If someone wants to look at the site, I have the info and they can log in.  
>> Or if they want to provide settings for me to triple check, that would be 
>> great
>> and 
>> if they have any ideas as to why its acting like it is, very much 
>> appreciated 
>> So far even though tech support has viewed in on Optics and have had some 
>> recommendations as to settings, its not fixed the issue.
>> 
>> thanks in advance,
>> 
>> jay
>> 
>> peltz power
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to